I'm working on a science project and there's one aspect of home wiring I need to find out (don't worry, I'm not messing with wiring - this is all on paper). Since 120V outlets in a home can be wired to either of the two 120V legs that come in from the power company, would it be a true statement that outlets on different breakers could be out of phase with each other? In other words if Bedroom 1 is tied to leg 1 and bedroom 2 is tied to leg 2 is it reasonable to assume that the sine waves measured from outlets in bedroom 1 will be out of phase with the sine waves measured from outlets in bedroom 2?

2
  • 1
    You may also like to know more about reactance. Reactance is where the current and voltage become out of phase, and in industrial applications with nonlinear loads this creates harmonic currents on the neutral.
    – Kris
    Jun 8, 2015 at 16:05
  • 1
    This is probably one of the most commonly misunderstood concepts in American residential power. Most electricians even get it wrong. Jun 10, 2015 at 13:35

6 Answers 6

13

Sort of. It depends on your frame of reference.

If you're looking at the ungrounded (hot) conductor from each receptacle, you'll end up with a 240 volt circuit. Since it's a single circuit, it can't be out of phase with itself. If you hooked up an oscilloscope to the ungrounded (hot) conductor of each receptacle, you'd get a single 240 volt sine wave.

If you're looking at the two separate circuits (e.g. the ungrounded (hot) and grounded (neutral) conductor from each receptacle), then you'll end up with two 120 volt circuits 180° phase shifted from each other. If you hooked up the oscilloscope to the ungrounded (hot) conductor and grounded (neutral) conductors from each receptacle (4 leads instead of 2), you'd see two 120 volt sine waves 180° phase shifted from each other.

The two sine waves should look something like this.

sine waves from single split phase transformer

Because the waves are phase shifted 180°, the electrical potential between the legs (at the peak) will be 240 volts. While the potential between either line and "neutral", will be 120 volts.

If the waves were not phase shifted, they'd be at the same potential (or have 0 volts between them).

in phase sine waves

So while this is not a multi phase system, it's also not a simple single phase system. Technically it's known as a "Single split phase system".

All of this; of course, assumes that the ungrounded (hot) conductors are from different legs of the service.

13
  • 8
    @DavidPfeffer Go hook up an oscilloscope. It's a single phase, with a center tapped "neutral". If you measure line to line, you'll see a 240 volt sine wave. If you measure line (L1) to "neutral" (N), you'll see a 120 volt sine wave. If you measure line (L2) to "neutral" (N), you'll also see a 120 volt sine wave. However, the two 120V waves will be shifted 180° from each other. So while one wave is peaking at +120V, the other will be peaking at -120V. I agree that "phase" might not be the best word, but the idea is the same.
    – Tester101
    Jun 10, 2015 at 13:48
  • 1
    Undownvoted based on the update. Jun 10, 2015 at 19:39
  • 3
    BTW its a bit misleading to show a scope graph with the y axis going to 120v since if you did that on a 120v RMS system (all household power in the US) the y axis peak would be ~172v. Handheld RMS meters would only ever show you 120 or 240, but that's a different way of measuring. If you want to show 120v on your scope graph you should shade the whole area under the waveform, since that's what mathematically equals 120v.
    – Jeff Meden
    Apr 7, 2016 at 16:06
  • 4
    @JeffMeden I agree, but I'm trying (and failing) to explain a concept. The numbers on the graph are meaningless, and are only included to make it more familiar to the general audience. If I wanted to be overly technical in my answer, I wouldn't have drawn the diagrams in crayon.
    – Tester101
    Apr 7, 2016 at 16:10
  • 2
    @ArchonOSX: Why would you "add up to zero"? Voltage is a difference.
    – GManNickG
    Apr 7, 2016 at 19:24
5

This is mainly a semantic question.

From an electrician's point of view, US household supply is a single 240V that can be split into two center-tapped hot legs.

From a mathematical or E&M point of view, the different legs have voltages that are 180º out of phase, and therefore I think it would be safe to call them two phases once they're separated.

(Left to the reader as an excercise: if you take a brick and cut it in half, do you have one brick or two bricks?)

4
  • 1
    I agree. We seem to be getting hung up on the meaning of the word "phase". It seems to me all the answers are saying the same (or similar) things, yet somehow some are being down voted while others are up voted.
    – Tester101
    Jun 11, 2015 at 1:19
  • 1
    They are only 180° out of phase if you first measure one from Neutral to Hot and then measure the other from Neutral to Hot since you are measuring them both in different directions. There is actually no phase displacement. Hence the term single phase.
    – ArchonOSX
    Apr 6, 2016 at 22:47
  • 1
    Can we just use the Wikipedia definition? "Phase difference is the difference, expressed in degrees or time, between two waves having the same frequency and referenced to the same point in time" if you measure each source of a residential center tap aka "split phase" to ground, the peak of 172v will be 180 degrees apart, plain and simple.
    – Jeff Meden
    Apr 7, 2016 at 15:58
  • 1
    If you take a brick and cut it in half, you will have a single split brick. Hence, single split phase. Jan 30, 2017 at 23:47
1

In a typical residential North American 120VAC, the answer is NO

The reason is your house only receives one phase, and thus that one phase cannot be out-of-phase with itself. Changing your frame of reference (by measuring voltage from the N rather than across L1 and L2) does suddenly not make them out of phase.

If your real question is: "Will the voltage measured from N to L1 always be shifted 180 degrees compared to the voltage measured from N to L2?" then the answer to that is "Yes"

...however that fact alone is not enough for it to be considered a separate phase of power.

If you truly had two phases, then the voltage difference between them would vary and occasionally be 0.

7
  • Sorry the OP is asking about the sinusoidal wave relationship between a transformer. The voltage is irrelevant. While one sinusoidal is 360° the split-phase terminology describes the relationship of the neutral at the 180° center point. The neutral has zero potential voltage because of the sinusoidal wave canceling out the other.
    – Kris
    Jun 10, 2015 at 14:13
  • 1
    Again, the voltage-waveforms may appear out of phase. I think that is covered in my statement of "Will the voltage measured from..." (which I will correct since it doesn't read well atm).
    – RobotAndy
    Jun 10, 2015 at 16:10
  • 3
    So frustrating I don't have enough credibility here to comment on the actual post, but the problem with the pictures posted by Tester101 on the other post is that there isn't a GREEN and BLUE line. There is only one line! If you truly had a green and blue line, you would at some point be able to measure 0V between them with your test equipment - but you can't! You will always have 240V difference between them, that's the subtle difference between split phase and real 180 degree two phase.
    – RobotAndy
    Jun 11, 2015 at 1:41
  • 1
    @RobotAndy If you use @ before a users name, the system will notify them directly.
    – Tester101
    Jun 11, 2015 at 15:51
  • 5
    @RobotAndy I'm confused by your last comment. You do understand that when you hook up a volt meter, you're actually measuring RMS voltage right? In my drawing, the BLUE line represents the voltage over time as measured between L1 and N, while the GREEN line represents the voltage over time as measured between L2 and N. I could have drawn an additional RED line, that could show the voltage over time measured between L1 and L2. In which case you'd see a sine wave with an amplitude of 240 volts. The period of my diagram is 1/60th of a second.
    – Tester101
    Jun 11, 2015 at 15:59
0

Yes. Technically they're 180 degrees out of phase if the transformer is 120/240 split phase. The neutral is tapped at the center of the coil and each side of the neutral is wound 180 out of phase from the other. A 120/208Y transformer would have each phase 120 degrees out of phase.

Edit: Here is a recent diagram I made to help illustrate the concept. enter image description here

2
  • I'm sorry, but this is incorrect. @RobotAndy has the right answer. To explain with an example, if they were 180 degrees out of phase, then connecting across the two phases would yield 0V, not 240V. Jun 10, 2015 at 13:34
  • 2
    You are mistaken. Please delete or update your comment as it is misleading.
    – Kris
    Jun 10, 2015 at 23:34
0

Using vector sums,

If we assume that V1 + V2 = VT

Where

V1 is from the center tap of the transformer to one phase (L1)

V2 is from the center tap of the transformer to the other phase (L2)

and L1 = 120 V at an angle of zero degrees

and L2 = 120 V at an angle of 180 degrees

and VT = the voltage sum of V1 and V2 (i.e., voltage across both phases)

Using Kirchoff's voltage law (i.e., going around the circuit)

VT = V1 + V2' = V1 + (-V2)

VT = (120, angle zero degrees) - (120, angle -180 degrees)

VT = (120, angle zero degrees) + (120, angle zero degrees)

VT = 240, angle zero degrees

The above math supports that the L1 and L2 are 180 degrees out of phase

1
  • You are presupposing that the phases are out of phase, so the subsequent math is only proving the presupposition- which is more precisely the underlying question (are the outlets (or legs, or bus bars in the panel) simply out of phase in a residential electrical system?). Now, if you had simply stated that 240V is measured (and calculated) by the difference between two voltage potentials, and that 120V minus negative 120V equals 240V, then the relevance of using measured voltage as proof that the phases were equal and opposite, could have been meaningful (but redundant per Tester101's answer). Apr 6, 2016 at 19:57
0

Voltages across each leg will be 180 deg out of phase....remember that voltage is a DIFFERENCE so if voltage across leg 1 to neutral (V1) is positive the other will measured negative (-V2) (out of phase by 180) relative to V1. (The numbers V1 and V2 are both positive numbers). Recall that voltage is a DIFFERENCE between two points. So we have V1- (-V2) which is 240 volts if both V1 and V2 are 120 volts. A Minus times a minus number is a positive number so V1-(-V2) = V1 + V2.

Richard MS physics, BSEE