We have a packaged HVAC on the roof and the AC needs to be replaced. It's 23 years old and dying/dead. We were considering buying just an AC and keeping the package unit running for heat.
We feel that the AC always dies first anyway so why buy another package unit when the gas furnace part of it is always still in good operation when the AC goes. On top of that, split-system AC units are always rated for a higher efficiency and we live in the Vegas desert so that is very important to us.
Are we being crazy? This means we'd have to split the ducting somehow. Also, when it's time to replace the furnace, where will it go? Can it go on the roof or will we have to change the gas piping, and the ducting again, to place the unit somewhere inside?
Is this a heat pump with supplemental gas heat?
Sounds like the shuttle valve is stuck or something in the cycle reversing has failed, heatpumps do both AC and heating.
Why double the misery by having two systems to fail and not having the current one repaired/replaced?
As to new systems, you can get very efficient heat pumps with supplemental gas heat, we just installed such a system in our business. During low level heat needs, it runs in heat pump mode, when the temperature outside drops below a certain settable level, the gas portion runs in tandem. The gas section is the new high-efficiency type that extracts so much heat that they use a PVC stack and water drain for the condensate. You'd kill two birds with one stone, having AC and more efficient gas heat.
You'd need an air-handler somewhere downstairs, taking up the same amount of space (and nearly the same cost) as a furnace. I can only assume that the increase in efficiency is due to having the unit being within the building envelope, instead of on the roof.
Do a full, new split system downstairs. I might endeavor to have the old unit remain as a back-up, with its ducts removed and a simple grate on the ceiling. Although, at 23yo it's got to be on its last leg, too.
IME, rooftop units are for when you want more than ~5 tons of AC, and don't want dual-split systems.
Edited excerpt from pitzersonehour.com: (short answer: packaged are cheaper to install and cost more to run, split systems; the opposite)
What’s the Difference Between Split System and Packaged Air Conditioners?
Split air conditioning system
Pros:
  • Greater energy efficiency possibilities
  • Split air conditioning systems have SEER ratings from 13 to 23.
Cons:
  • Labor costs more because you are installing a unit outside the house and also inside (usually in the attic or crawlspace, depending on the type of air handler). Also, the system can’t be charged with refrigerant until it has been set in place, which adds to the cost.
When you’d want this: It’s a more cost efficient choice if your home already has a [reliable] furnace, and you are purchasing a new air conditioning unit or replacing an older unit.
Packaged air conditioning system
Pros:
  • Space efficiency - Unlike split-system units, the package unit has all the components in one place.
  • Cheaper installation - Since packaged units can come pre-charged with refrigerant, and they are only installed outside, installation is cheaper than a split unit.
Cons:
  • Limited energy efficiency: Packaged units typically have a SEER rating from 10 to 18.
A company I work for will up-charge you if it's a horizontal attic install or in a crawl space ('cause that ain't fun and does require more work).
  • One note about "cheaper installation" -- if you're talking about rooftop installation, a package unit will almost ALWAYS require the services of a VERY expensive crane. A standalone condenser unit is somewhat negotiable crane-wise if the installer is willing to be creative (like a mini-crane that mounts to the ladder itself). Packaged systems are SO heavy, getting it up on the roof is just the FIRST problem... you still have to move and lift it into position around once it's up there.
    – Bitbang3r
    Sep 10, 2019 at 22:50