0

I'm installing a GFCI Outlet in the bathroom using 12/2 wire on a 20 amp breaker.

The outlet box contains GFCI Outlet, 1st Switch to control light/Exhaust Fan in ceiling, 2nd Switch to control vanity light above sink.

I have a closet in the bathroom which has an outlet box with both 12/2 and 14/2 running to the box. This is the end of the circuit.

1
  • Can you provide a list of all the wires in each box, also noting their grouping? A few photos of the wires would also be useful. – Tester101 Apr 24 '15 at 18:09
1

First, the 14/2 wire will need to be upgraded to 12/2 wire or you need to downgrade the breaker to 15 amps to protect that section 14/2 wire from possibly overheating/causing a fire.

The vanity typically does not need to be on the GFCI but if the light/exhaust fan is close enough to the shower/tub that you can touch it (if you are not tall enough, image if you were tall enough) while standing in the shower/tub then the light/exhaust fan should be protected by the GFCI. The closet does not been to be protected by the GFCI, but it wouldn't hurt if it was.

GFCI receptacles have two different sets of terminals. One set will be marked line, this is where power from the panel is connected, and other other set is load. The load terminals will protect any outlets downstream that are connected to this.

For anything protected by the GFCI, the neutrals will need to connect to the load neutral terminal. Same as for the hots as well, they need to be connected to the load hot terminal. But in the case of the fan (if it needs to be protected), wire the hot terminal to one of the switch terminals and the other switch terminal to the hot on the fan. The neutral will just be wire directly to the load neutral. If any downstream device does not feed the neutral back through the load terminal on the GFCI, the GFCI will trip.

2
  • 2
    When referring to terminals on devices, "upper" and "lower" is almost never helpful. Not all devices are configured the same, and there's not always an "up" or "down". When talking about GFCI terminals, "line" and "load" is the way to go. – Tester101 Apr 24 '15 at 18:14
  • @Tester101, you are right. I thought I put in my answer the two different types of terminals on the GFCI (line/load) but it appears I completely forgot it. Will edit and use your suggestion as well. – diceless Apr 24 '15 at 18:29

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service, privacy policy and cookie policy

Not the answer you're looking for? Browse other questions tagged or ask your own question.