The 2014 NEC uses "physical damage" at various points to refer to well, hard knocks, if you know what I mean. However, certain passages in the NEC, such as 358.12 point 1 on EMT:
Where, during installation or afterward, it will be subject to severe physical damage.
380.12 point 3 on multioutlet assemblies:
Where subject to severe physical damage
and 388.12 point 2 on surface nonmetallic raceways:
Why is it that the NEC changes the terminology for these and a few other wiring methods, and what is the difference between plain ol' physical damage and severe physical damage, or is that left to the AHJ to decide?
P.S. if it helps -- I'm trying to decide whether surface nonmetallic raceway would be suitable for a branch-circuit extension in a residential attached garage, or if I need to use something sturdier, such as schedule 80 PVC, as I'd much rather not rip into the garage walls.
  • I am still trying to figure out the power above heater thing. You ask great questions.
    – Some Guy
    Mar 26, 2015 at 23:03
It's up to the AHJ to make the call. The term is used to express that some methods and materials offer better protection against physical damage, and that those methods and materials should be preferred when there's potential for greater than normal physical damage.
I'd suspect you wouldn't encounter severe physical damage in residential settings often, though it may be more common in industrial settings where there is equipment and machinery moving hither and thither.
After further research, it appears the term was approved at some unknown time. It was possibly written in as part of the original proposal for an article, and then propagated as similar articles were proposed.
There have been proposals to apply the term to other areas of the code. Though as far as I can tell, all such proposals have been rejected. The outcome of one such proposal can be found in this document, where the submitter proposes a revision to 330.12(1) to include the term.
The uses not permitted section of Article 330 should acknowledge the protection against physical damage provided by the metallic covering of this wiring method by limiting the cable from use where it is subject to severe physical damage (such as forklift or vehicular damage). The degree or magnitude of physical damage depends on the wiring type and the likelihood that damage prior to or after installation could severely damage or cause the wire to be inoperable. Type MC Cables have a metallic covering which provides protection to the inner insulated and non-insulated conductors against physical damage before, during, and after installation.
While the term “severe physical damage” in not defined in the NEC and thus requires evaluation by the AHJ, the phrase is used to qualify the suitability of several wiring methods including in 358.12 for EMT, in 368.12 for busways, in 370.7 for cablebus fittings, in 376.12 for metal wireways, in 380.12 for multioutlet assembly, in 386.12 for surface metal raceway, in 388.12 for surface nonmetallic raceway and in 392.12 for cable trays.
A comment from one of the folks who voted to reject the proposal, basically points out that the term only currently applies to raceways and wireways not cables.
... The submitter’s comparison to articles 358, 368,370, 376, 380, 386, 388, and 392 all include wiring methods or systems that are unique from that of cable either by virtue of limited use or they are metal raceways or wireway. Cables introduce a significant degree of flexibility in the manner and location that they are routed and the proliferation of their use within the industry.
Everybody involved agrees that the term is undefined, subjective, and the final determination as to if it's "severe" physical damage is left up to the AHJ.
I don't know for certain but my interpretation of that language would be that "severe physical damage" would result from impacts or accidents caused by machinery, and "physical damage" would be an impact or accident involving people and objects only. For example, a forklift or pallet jack could easily crush even heavy-walled Rigid Metallic Conduit (the stuff with threaded ends and connectors). However if you had EMT conduit on the wall and a leaning 2x4 falls against it, it will probably be fine.
  • Well, there aren't any forklifts or pallet jacks in my garage, but there is the off chance the family car could fender-bender into it...or is it legitimate to use a wiring method not specified for severe physical damage in an environment where severe physical damage is precluded solely by the routing of the wiring? (Good luck smacking a raceway 6'+ off the floor with a car...) Mar 26, 2015 at 23:45
    Ohh, boy @ThreePhaseEel is gonna put airbags in his car so he can hit the raceways in his garage by hopping! Be sure to take video! If it's out of reach of the car, it's not subject to severe damage. Frankly, I don't think even one right at bumper level really qualifies - a car bumper is not a forklift fork, or a flying lathe chuck, or something else hard, unyeilding, and massive enough to shear conduit. Sure, you'll damage conduit at bumper level if you drive right through the wall, but there are limits to what is reasonable to protect against - and moving it out of bumper level does that.
    Mar 27, 2015 at 1:46
The easy out answer is 'whatever the AHJ says'
In an attempt to be useful:
Severe, as a modifier here would seem to require a severe environment.
Anything that can be provisioned in a R3 Nema Enclosure is clearly not designed for a severe environment.
Nema Enclosures
3S - requires that the external mechanism(s) remain operable when ice laden.
3X - requires a level of corrosion protection
4 - adds hose directed water
5 - adds dust, lint and fibers
6 - includes a classic group of adjectives 'occasional temporary' and 'limited' with respect to submersion in water
'Severe damage' and 'fork truck' seem to often be found in the same sentence. Grain silos, switch gear, and industrial locations, also seem to be places where severe conditions exist.
I do not think that there is a reasonable expectation that 'severe damage' can occur in or on a residential structure, past the point of customer demarcation