This 5 minute task has kept me busy for an hour. Old switch/outlet combo melted. Replacing with gfci combo.

Red/White pair is the line. Orange/White pair is the load to the light.

enter image description here

Strangely, this outlet says its load and line are flipped, with the line on top instead of the bottom.

enter image description here

Wiring this way got me a dead outlet. Wiring with the load on top got a green light, but it won't reset and light won't turn on.

enter image description here

What's the correct wiring please?

UPDATE: This is a Leviton X7299-W switch / outlet combo. Here's a link to a pdf of the instructions: !4

When running just the line ( red / white ) pair to the bottom posts, I get a green light, but it won't reset and no power.
https://docs.google.com/file/d/0B_FzlcEZYP_PX25GT2o0NUl6b2c/edit?usp=docslist_api

Note that this is the bottom terminals, because all the diagrams I've seen show the line at the bottom, load on top, and if I run them to the top, I get a dead outlet. No green light, no power, won't reset. If the green light is an indicator of anything, it would appear that the bottom posts are closer to the truth, although it also appears that this outlet can't handle the truth...

7
  • Possible duplicate
    – Tester101
    Mar 23, 2015 at 1:21
  • You say that "Red/White pair is the line", yet in the last photo you show the "red" wire connected to the "bottom" LOAD terminals. You also don't show where the switch wires are connected.
    – Tester101
    Mar 24, 2015 at 14:31
  • @kmunky -- can you post the model number or a link to the install instructions for your GFCI switch/outlet combo? Mar 24, 2015 at 22:09
  • I am not seeing the ground wire coming out of the box. Was the original device ungrounded? That could partially explain the GFCI issue. Strangely enough, I just wired a combination switch/outlet yesterday. However, it did not have GFCI and the wiring layout was completely different. A tip you should take seriously is to not put more than one wire in a screw terminal. Your neutral wires (white) should be twisted together and wire nutted with another short piece of white wire of the same gauge. Then the 3rd wire can be connected to the outlet. This is called a pigtail and is very widely used. Jul 27, 2015 at 19:54
  • 1
    Diagrams are designed to illustrate theories and ideas, following them blindly can get you into trouble. If a diagram shows LINE and LOAD differently than what you have. Use the terminal labels for reference, not "top" and "bottom".
    – Tester101
    Oct 25, 2015 at 18:48

4 Answers 4

2

What this thing is

It is a triple GFCI, switch, and receptacle.

The onboard receptacle is hardwired internally to be on the protected side of the GFCI - no choice there.

The GFCI portion has LINE inputs and LOAD outputs like any other GFCI. Most GFCIs ship with a piece of tape over the LOAD terminals that says "Do not remove unless you really know what you're doing." Seeing 4 screws on the old thing and 4 screws on the new thing does not qualify as knowing what you're doing. Put a piece of tape over the LOAD terminals.

It is also a switch. The switch does not have any terminals. It has 2 wires. The switch shorts the two wires. That is all.

Phase 1: the receptacle

Don't even think of hooking up all the wires at once and having it magically work. It won't.

First, hook up exactly 2 wires (plus ground, I won't mention ground again). 2 wires only. Only to the "LINE" terminals. This will power up the receptacle only, and will do nothing for the light.

Victory is defined by the receptacle working, the neutral (tall) pin on the receptacle being near ground potential (no neutral/hot reverse) and the TEST and RESET buttons both work. (if they don't work, you messed with the LOAD terminals! Naughty naughty!)

Phase 2: the lamp

Now there should be 2 loose wires coming from the wall. Those are switched-hot (black or a color) and neutral (white) to the lamp. We switch hot, so wire-nut the switched-hot from the lamp to either one of the black wires from the switch. That was easy.

Two wires still dangle unattached. One of them is neutral to the lamp. The other is always-hot from the switch. (it becomes switched-hot at the switch.) They are coming from different things, but functionally, they're a matching pair. What do you do with an always-hot/neutral pair? Connect them to a matching hot-neutral supply pair.

And look what we have on the GFCI's "LINE" terminals: always-hot and neutral.

Those fancy "screw-and-clamp" types take 2 wires. So there's room.

Once that is done, victory is defined by the light working off the switch. And the GFCI not tripping unless you push the TEST button or plug something into it.

Phase 3: the GFCI

Oh? You want to GFCI protect the lamp as well? People often don't bother... but sure, why not. After all, there is a GFCI device right here, and it certainly is capable of protecting downstream loads. It has a matching pair of hot and neutral terminals for that exact purpose: the LOAD terminals. The ones with the tape that says "... really know what you're doing."

Since you understand "matching pair of hot and neutral"... close enough.

Connect that pair we discussed to the GFCI's pair of LOAD terminals instead of its pair of LINE terminals.

If you want to see what a GFCI does, then hopscotch them: connect the hot to LOAD and the neutral to LINE or vice versa. It's wrong, but it'll give you an education.

Once it's hooked up correctly, and the GFCI trips, what does this mean?

  1. The GFCI must be defective, surely!
  2. The lamp or its wiring has a ground fault.

You can pursue #1 but usually it boils down to #2. Not a 5-minute job.

0

From the symptoms you described, it could be one of three things, as you had it wired correctly the first time around:

  1. Your GFCI switch/outlet needs to be reset (and perhaps toggled as well) in order to start functioning.
  2. You made a bad connection to the GFCI switch/outlet on the line side when you originally wired it.
  3. Your GFCI switch/outlet is somehow dead -- I'd call that unlikely though considering it reacted as it should to an attempt to power it up via the load terminals.

UPDATE: Based on your additional information -- I'd try flipping the switch first, then if that doesn't get your outlet on, I'd swap it for another one

1
  • The gfci won't reset. The old outlet had a weird wiring: line hot lead top, orange top negative post, and negative lead was pig tailed to negative post. Hot load post was open. This resulted in a green light on outlet, and ceiling light flicking itself on/off at about 1/2 second intervals. The configuration shown (pic 3) is closest to operational, but still won't reset. (Not sure what you mean by toggle.)
    – kmunky
    Mar 24, 2015 at 13:54
0

First, verify that your red/white pair is the line by connecting it to the line (top) terminals on the device. Cap the orange/white wires and energize the circuit. The outlet should work, possibly after pressing the Reset button.

Assuming your light doesn't require GFCI protection:

  1. Make a pigtail with white wire and connect the pigtail to the two existing whites with a wire nut, then connect the pigtail to the white line screw.
  2. Make a pigtail with black wire, and connect the red wire, one of the two switch wires from the top of the device, and the pigtail together, then connect the pigtail to the black line screw.
  3. Connect your orange wire to the other switch lead.

The load terminals will be unused, and they are used for downstream devices that require GFCI protection.

If the light does require GFCI protection,

  1. Red and white to the line terminals
  2. White from the light to the load white terminal
  3. One switch wire to the load black terminal
  4. One switch wite to the orange wire
0

How you wire it up, depends on whether or not you want to provide GFCI protection to the load. This answer will show you how to wire it up in either case.

GFCI Protecting the Load

Wiring Ground Fault Circuit Interrupter Switch enter image description here

With this arrangement a receptacle, switch and disposal are protected with the ground fault breaker built into the device.

Not GFCI Protecting the Load

Wiring Ground Fault Interrupter and Light Switch enter image description here

With this arrangement the receptacle is protected but the switch remains outside the circuit. This arrangement can be used to control a light or other device where the extra protection of a gfci is not necessary.

Make sure you follow the labeling on the image, and not base your connections on "top" or "bottom" terminals.

6
  • Saw that before posting, should have mentioned, sorry. Neither of those configurations resulted in a green light, reset didn't work, and no power to outlet or switch. completely dead outlet in both cases.
    – kmunky
    Mar 24, 2015 at 13:57
  • What is the make and model of the GFCI/switch combo you're installing? Are you sure your assumptions about where the wires go is correct?
    – Tester101
    Mar 24, 2015 at 14:26
  • Start by just connecting the "line" wires to the Line terminals, and see if that works.
    – Tester101
    Mar 24, 2015 at 14:27
  • The diagrams in the linked answer appears to refer to a different device that has the line and load terminals reversed from this one; following one of the two scenarios shown while adjusting for that change should do the job.
    – TomG
    Oct 25, 2015 at 18:02
  • 1
    @tester101 I was trying to point out that the labels should be followed, not the top/bottom positioning. Either way, the OP needs to follow the labelling, not the position. Those diagrams are pretty decent.
    – TomG
    Oct 25, 2015 at 18:56