In a bath in my house I currently have a very old (likely original 1949) outlet/switch combo. The outlet is hot, not dependent on the switch being on. The switch controls vanity lights. I would like to replace the outlet/switch combo with a GFCI outlet and a separate switch for the vanity lights (and so also move from one a one gang box to a two ganb box).

My question -- without knowing exactly how this is wired (have not tore it apart), is this likely to be an option? Will it only work if there is two wires feeding the current outlet/switch? Assuming there is only one wire, does anyone have a diagram on how this would be wired? If it cannot be done, is there GFCI/switch combos?

As a footnote...the wiring in the house is original as well, on the list of things to get done, but just not in the budget for a few years. It is non grounded 2 wire.

Thanks!

1

I had a similar situation in my bathroom. I had power in the ceiling, to the light, and a 14/2 running down to the switchbox. My assumption is that the original install consisted only of the light switch, but had been "Upgraded" by everyone's favourite contractor, Some Moron. This esteemed craftsman put in a combo switch/receptacle, Jumpered the hot side of the switch to the hot side of the receptacle and then pigtailed the neutral of the receptacle to ground.

IF THIS IS YOUR SITUATION,

You need to run a new 14/3 from the ceiling to my switch location and break drywall to install a 2 gang box. The final wiring is:

Panel Black - 14/3 black. (with pigtail in switch location) Light Fixture Black to 14/3 Red. (Switched Hot - power to light) Panel White - 14/3 white.

In the 2 gang box, I took a black from the pigtail to the GFCI hot, and the white from the 14/3 to the neutral screw.

Other possibilities:

Existing 14/3 -- Do as above, but obviously you don't need to run a new cable. Check the wiring in the light box to make sure you get the switched hot right.

Double 14/2 - In this situation, you'd have 1 14/2 powering the receptacle, and another 14/2 acting as the runner for the switch. Usually black is hot, and white is switched hot. The white wire should be marked as such, perhaps with a piece of tape on the end. Wire it exactly as it is.

Power to the switch box You may have the situation where the power feed from the panel goes directly to the switch box. Usually you'll have a feed from the bottom (power) and another pair going out the top to the light. Check these with a voltage tester!

Create a pigtail on the feed black with two short pieces of black wire. One goes to the switch, the other to the receptacle. To the other side of the receptacle, attach the black to the light. This is your switched hot.

The white from the light, the white from the feed are wired together with an additional short piece of white wire which goes to the neutral of the receptacle.

Additional Warnings:
All connections go to the LINE side of the GFCI.
Do not work with power on. Turn off the breaker or fuse.
If you don't see one of the scenarios presented here, then call for professional help.

  • Actually, there's plenty of good reason to, and no good reason not to, run the light off the "load" terminals of the GFCI. – Ecnerwal Dec 3 '14 at 16:16
  • Not if the Neutral is up in the ceiling. Then you'd have to run ANOTHER wire. So it only works if Power is to the switch box. – Chris Cudmore Dec 3 '14 at 16:19
  • Thanks for the response Chris, and sorry for the delay in accepting! – Jay Dec 7 '14 at 13:08