I have this one outlet in my house that, when exposed, has three wires protruding from it (while there are two wrapped in a nut). As far as I can test, two are feeding power and one is acting as a feed/neutral. One of the power source wires is controlled by a two-way switch, while the other one is controlled by a three-way switch. That three-way switch (along with the other three-way switch) controls the chandelier in the house. There is also a light outside our front porch that is controlled by a two-way switch and is somehow tied to the outlet because when the outlet isn't wired correctly, neither the chandelier nor the outside lights work.

Right now, the outlet is wired so that one hot wire (black coating) is connected to the hot side (right side) of the outlet, while the other two (both in white coating) are connected to the neutral side (left side). With this configuration, the outside lights work, the chandelier works only when one three-way switch is on and the top outlet works on and off with the two-way switch but the bottom part of the outlet doesn't work at all. I really do apologize for the VERY long-winded question but there are so many nuances that I don't know how to be more succinct.

With this configuration, is there any way to not have both outlets feed off switches? enter image description here enter image description here

  • 2
    Pictures? What color are the nutted wires? Sounds like the tab may be broken to separate top and bottom at least on the hot side. If only one 3-Way works the chandelier, something is wrong there. – Ecnerwal Oct 20 '14 at 21:12
  • The nutted wires are one black, one white. – mjt117 Oct 20 '14 at 21:31
  • 2
    If you're not comfortable with electricity, please ensure you have a firm grasp on it before proceeding, or call an electrician. Do not risk harming yourself, others, or your property. – rjbergen Oct 20 '14 at 22:40
  • 1
    You haven't asked a long-winded question; you've told a story but there is no question here. What is your question? And to repeat what Ecnerwal said: once you have sorted out what your specific question is, please post photos of everything, along with where in the world you are. Different countries use different colours for wires. – Eric Lippert Oct 20 '14 at 23:23
  • goo.gl/BwzrFm – mjt117 Oct 21 '14 at 14:32
1

OK, first of all, plainly this is a mess. The fact that there is a white wire hooked up to a black wire without any recolouring of it alone says that (1) there's some amateurish stuff going on here, and (2) you cannot trust any of the white wires to actually be neutral until you prove that they are. So proceed cautiously, and take notes as you go.

There are a lot of questions here but a good one is:

What's the easiest way to track a specific wire to see how it flows without ripping out the walls?

Start by obtaining a long three-prong extension cord. Plug it into an outlet that is on, and verify with a voltmeter that there is voltage between the hot and neutral, there is voltage between the hot and ground, and no voltage between the neutral and ground. You now have an extension cord which you can use to provide a known ground and a known hot.

Next, turn off the power to everything that you're going to be working on.

Next, put a piece of tape with a number on every wire that you're going to be working on, and start making notes about the color and location of each numbered wire end, and what they're hooked up to now. Take photos. You want to be able to put this back together the way you found it later. Number the switches as well.

Next, carefully get all the wire ends exposed but not touching anything, and turn the power back on. Use your known ground and your voltmeter to determine which wires are hot under every combination of switches. Remember, some of the whites are hot.

Turn the power back off again.

Test everything again to make sure that no, really, the power is off.

Now test everything again against the known hot to find out which wires are neutrals that run back to the panel. Again, test everything against all combinations of switches, remembering that at least one mistake has been made in this wiring so far; there might be more. Interrupting a neutral with a switch is almost always wrong, but I have found plenty of interrupted neutrals in old houses.

Now unplug your extension cord from the wall and get a flashlight. Rig yourself up a continuity tester out of the extension cord and the flashlight. (Of course if your voltmeter has a continuity tester, use it instead of jury-rigging one out of a flashlight.)

Suppose you suspect that wire ends labeled 2 and 9 are the same wire. Attach end 2 to the extension cord ground. Run the extension cord to the other. Now wire the extension cord to the battery, the battery to the light, and the light to end 9. Did the light go on? Then your hypothesis is confirmed. Did it not go on? Try every combination of switches. Again, record your observations.

Keep doing that until you have enough observations to form a consistent theory of how the wiring runs through the walls. Draw a diagram.

Once you're there, you should be able to solve your problem. If you cannot, then you'll be able to post a question here with a lot more information.

Also, take this opportunity to ensure that every wire is correctly coloured, by putting tape on miscoloured or confusing wires. Also, if there are oddities such as a box that has hot wires from two different breakers, make a note of that for the next guy.

  • Can you elaborate a bit more on this? "Next, carefully get all the wire ends exposed but not touching anything, and turn the power back on. Use your known ground and your voltmeter to determine which wires are hot under every combination of switches. Remember, some of the whites are hot." – mjt117 Oct 21 '14 at 20:08
  • @MarkTraina: A voltmeter will only tell you that there is a voltage when it is part of a circuit. If you touch a voltmeter probe to a hot wire but do not touch the other probe to anything, that tells you nothing because there is no circuit. If you touch it to a piece of metal that is not grounded, that's not different; the probe is already a piece of metal that is not grounded. To test whether something is hot, you need a known ground. And conversely, to test whether something is grounded, you need a known hot. – Eric Lippert Oct 21 '14 at 20:22
  • @MarkTraina: There are lots of videos on the internet on how to use a voltmeter; if you're going to be diagnosing electric circuits then knowing how to use this tool correctly is going to be important, so I would start there. – Eric Lippert Oct 21 '14 at 20:24
  • I think I understand, so the extension cord acts as the known ground when testing to figure out which wires are line wires and then also acts as the known hot when testing the neutral wires? So the cord stays plugged in to an outlet that is not on the same breaker as the ones I am currently testing. – mjt117 Oct 21 '14 at 20:49
  • @MarkTraina: That's right. The safety ground of course is never interrupted in a correctly wired box, but again, you don't know whether the wiring you are investigating is correct. That's the point of the investigation. So proceed carefully deducing new facts starting from known facts, like "this is a good ground, this is a good hot". – Eric Lippert Oct 21 '14 at 21:19