I thought wall receptacles required a 20 amp breaker. Am I wrong?

5

Answer based on the NEC in the US.

In some areas with local amendments to the NEC maybe, but it's not an across the board code requirement.

There are areas in a home that do require 20A circuits, such as bathroom receptacles, laundry receptacle(s), kitchen/DR/pantry receptacles. Other areas such as garages, utility rooms and unfinished basements it is definitely a good idea.

Personally I do most receptacle circuits on 20A, but this is not a hard and fast rule for me.

3

'T'-bladed 20a receptacles must be on a 20a breaker.

A 15a simplex outlet (where it only accepts a single plug) must be on a 15a breaker.

Standard 15 and 20 amp duplex receptacles (slots for two cords) may be protected by either 15's or 20's.


Is using 15 amp components on a 20 amp breaker against code? Provided it's not a simplex outlet (or as long as there is "2 or more" outlets on the circuit), code allows this.

www.inspectionnews.net, 20 amp duplex receptacle on a 15 amp circuit? Outlets rated for 20a is fine, a 20 amp outlet with a T slot, is not.

  • You can have single 15 amp outlets minimum of 2 on a 20 amp circuit, the statement at the top , the edit looks to have corrected this but it could be confusing to someone that doesn't know code. See table 210.21.b.2 – Ed Beal Feb 8 at 18:43
  • "minimum of 2"... iirc, if there's only a single simplex outlet on the circuit, it has to be a 15. – Mazura Feb 12 at 16:00
  • A single duplex is 2 outlets so this would be code compliant on a 20 amp circuit. – Ed Beal Feb 12 at 17:23
2

The maximum breaker size is determined by the wire size—not the type of outlet. It is okay to install a smaller rated breaker than the wire can carry, though that may be confusing to future owners.

For example, 10 gauge copper normally has a 30 amp breaker. However, it is perfectly fine to use a 25, 20, 15, or even a 10 amp breaker on 10 gauge.

Likewise it is safe (but a bit odd) to install a 50 ampere rated outlet on a 15 amp breakered circuit. One might do this for connector compatibility with say an RV or boat cord especially when you know the maximum load in the vehicle will be within range of the circuit.

But it would not be safe to change the breaker to 50 amps to match the 50 amp outlet if the wire is smaller than 6 gauge.

  • We have some computer equipment with 6-20P's with around 2A max current draw, just for an actual example of oddly corded equipment. – Jestep Oct 16 '14 at 19:57
  • Not true. A 20 amp outlet requires 12awg wire and a 20a breaker per NEC table 210.21.b.2 . A 50 amp outlet requires a 50 amp circuit per NEC 210.21.b.3 – Ed Beal Feb 8 at 18:39
  • @EdBeal: Re-read what I wrote. It is the wordy version of "It is okay to overprotect wires and outlets." – wallyk Feb 8 at 18:55
  • No you said it would be weird to put a 50 amp on a 15 amp breaker this is a code violation , the same as code dictates what size breaker, code is specific on the size circuit per outlet but you can use larger wire. The outlet size also dictates the minimum / maximum breaker size for the circuit as the tables explain so I see several errors. Yes I did read several times prior to posting. – Ed Beal Feb 8 at 19:42