It worked a couple of days ago but today the fan blows but the burner doesn't seem to come on. The status indicator inside the access panel flashes four times but I can't find any reference to tell me what that means.
  • Is it the blower fan running, or the draft inducer? Do you have the owner's manual? From the limited info I could find, 4 blinks could be an open high limit. This would be consistent with the blower continuously running with no flame. – Tester101 Oct 12 '14 at 17:02
  • Definitely the blower. The is cool coming out of the vents. I have the "User's Information Manual" which seems to have no useful information. – Chris Nelson Oct 13 '14 at 21:27
  • After having it off for ~30 hours it is working again. For now. Burner is lit and there is warm air coming out the vents. – Chris Nelson Oct 13 '14 at 21:32
A dirty air filter will cause that fault... not enough air flow through the heat exchanger resulting in "open high limit". (Embarrassed to say , I let that happen last winter).
| improve this answer | |