I'm replacing the wiring from a vintage chandelier and need to know what gauge wire to use. There are five lights on it. This is for the fixture only!
3 Answers
18g stranded wire is quite common on arms 14g stranded is often used to join the 18g arm strands, and to tie into the ceiling.
This applies to North America and normal chandeliers with relatively low (<50 each) wattage bulbs.
-
Please don't answer questions until the asker has clarified what the question is. Making the wrong assumptions could kill someone. Commented Oct 2, 2014 at 20:54
-
5Chandeliers usually use 18g for the arms (thisoldhouse.com/toh/photos/0,,20267510_20599803,00.html) and (at least the ones from HD) use in the ceiling. 14g is rated for 15 amps, and no chandelier Ive ever seen comes anywhere near that.– gbronnerCommented Oct 2, 2014 at 21:46
If you're in the US, NEC likely applies. Article 402 covers fixture wires, and explains what types and sizes are allowed.
Type
Table 402.3 lists the types of wires allowed to be used as fixture wires. If you're going to rewire the fixture, you'll have to use a type of wire listed in this table.
- FFH-2
- HF, HFF
- KF-1, KF-2, KFF-1, KFF-2
- PAF, PAFF
- PF, PFF
- PGF, PGFF
- PTF, PTFF
- RFH-1, RFH-2, RFHH-2, RFHH-3
- SF-1, SF-2, SFF-1, SFF-2
- TF, TFF
- TFN, TFFN
- XF, XFF
- ZF
- ZFF
- ZHF
Size
Table 402.5 lists the allowable ampacity for different sizes of wire. You'll want to use a wire that's sized properly for the load you'll be serving. In most cases, the maximum bulb size you'll have to account for is 100 Watt. Which means you'll likely only be looking at about 833 mA (100 Watts/120 Volts), so you can probably get away with 18 AWG wire.
402.6 says that fixture wires cannot be smaller than 18 AWG, so you'll have to use at least that size wire.
Overcurrent Protection
402.12 points to 240.5 for overcurrent protection of fixture wires, which tells you what size overcurrent is required for different sized wires. 240.5(B)(2) lists the size and length of fixture wires, when connected to circuits with various sizes of overcurrent protection.
National Electrical Code 2014
Article 240 Overcurrent Protection
I. General
240.5 Protection of Flexible Cords, Flexible Cables, and Fixture Wires.
(B) Branch-Circuit Overcurrent Device.
(2) Fixture Wire. Fixture wire shall be permitted to be tapped to the branch-circuit conductor of a branch circuit in accordance with the following:
(1) 20-ampere circuits — 18 AWG, up to 15 m (50 ft) of run length
(2) 20-ampere circuits — 16 AWG, up to 30 m (100 ft) of run length
(3) 20-ampere circuits — 14 AWG and larger
(4) 30-ampere circuits — 14 AWG and larger
(5) 40-ampere circuits — 12 AWG and larger
(6) 50-ampere circuits — 12 AWG and larger
Conduit/Tube Fill
You may also have to refer to Table 1 of Chapter 9, to determine the maximum number of wires that can be in a conduit or tube.
-
It would be nice to know what the down vote was for. I'm here to learn too, and that's difficult to do when folks don't point out your mistakes. Commented Oct 4, 2014 at 14:59
Agree 18 awg for the arms and 16 awg is desirable for a splice if needed to feed the ceiling junction box although 18 awg could be used by code as long as the total current stays below 6 amps. House wiring must be at least 14 awg or larger. The thinner gauge 18 and 16 awg is allowed because the wiring is not buried in a wall and is not adjacent to flammable materials. It must be "fixture wire" with quality high temperature insulation; doorbell or speaker wire is not likely to have this type of insulation.