I am making a Steampunk style lamp with black pipe. My intention is to use three lamp sockets as part of the design. I will have one cord coming out of the lamp as the plugin. However, I am not sure the safest way to splice the wires inside the black pipe. Tons of examples online of these Steampunk style lamps, but no information on safe wiring.
Same way you splice outside the lamp: Twist, cover with wire nut to compress and hold the twisted wires to ensure good connectivity, wrap all of that with a bit of electrical tape to help ensure that even if it comes lose it won't contact the pipe.– keshlamSep 27, 2014 at 20:21
2Gut reaction is that a crimp connector would be better than a wire nut. Best to keep all connections in an accessible place, like the base, so you can easily fix/verify they are still connected should you have troubles down the road. All metal parts should also be grounded as well, ensuring that if a wire does come loose, it blows the breaker.– gregmacSep 28, 2014 at 6:53
1A crimp will save on space versus a wire nut. But I would say either would be fine as long as you use the proper size wire nut or crimp. That is probably the most important part, right along with taking the time to make sure it is done properly. I would also heat shrink or tape the splices too.– EdwardtSep 29, 2014 at 0:40
1 Answer
The requirements for luminaires (lamps, light fixtures) are in Section 410 of the NEC. In particular, for mechanical strength, we should start with 410.38(A):
Tubing for Arms. Tubing used for arms and stems where provided with cut threads shall not be less than 1.02mm (0.040 in.) in thickness and, where provided with rolled (pressed) threads, shall not be less than 0.64mm (0.025 in.) in thickness. Arms and other parts shall be fastened to prevent turning.
Your black iron pipe should meet this requirement with ease -- most of it will be Schedule 40, which has plenty of wall thickness. Just make sure that you have all joints securely tightened (wrench tight, not just finger tight)!
You will also need a bushing (or clamp) of some type to protect the cord from strain where it exits the pipe as per 410.44:
Cord Bushings. A bushing or the equivalent shall be provided where flexible cord enters the base or stem of a portable lamp. The bushing shall be of insulating material unless a jacketed type of cord is used.
Now, to what you asked about, which starts off in sections 410.22 through 410.24 and 410.28 of the Code.
Luminaire (Fixture) Wiring -- General. Wiring on or within fixtures shall be neatly arranged and shall not be exposed to physical damage. Excess wiring shall be avoided. Conductors shall be arranged so that they are not subjected to temperatures above those for which they are rated.
Polarization of Luminaires (Fixtures). Luminaires (fixtures) shall be wired so that the screw shells of lampholders are connected to the same luminaire (fixture) or circuit conductor or terminal. The grounded conductor, where connected to a screw-shell lampholder, shall be connected to the screw shell.
Conductor Insulation. Luminaires (fixtures) shall be wired with conductors having insulation suitable for the environmental conditions, current, voltage, and temperature to which the conductors will be subjected.
This all should be obvious to you: don't cook, snag, stretch, or snake your wire, and use the right size -- as you mentioned three lampholders, we can presume that you're using medium base as that's what household light bulbs use, which leads us to a maximum of 300W, or roughly 2.5A of current -- 18AWG TFFN fixture wire can handle this with ease (its ampacity under the Code is 6A as per table 402.5), and is rated to 90 degrees C. Also, wire up your lampholders correctly (reverse polarity lampholders are real people-zappers)!
Protection of Conductors and Insulation.
(A) Properly Secured. Conductors shall be secured in a manner that does not tend to cut or abrade the insulation.
(B) Protection through Metal. Conductor insulation shall be protected from abrasion where it passes through metal.
(C) Luminaire (Fixture) Stems. Splices and taps shall not be located within luminaire (fixture) arms or stems.
(D) Splices and Taps. No unnecessary splices or taps shall be made within or on a luminaire (fixture).
FPN: For approved means of making connections, see 110.14.
(E) Stranding. Stranded conductors shall be used for wiring on luminaire (fixture) chains and on other movable or flexible parts.
(F) Tension. Conductors shall be arranged so that the weight of the luminaire (fixture) or movable parts does not put tension on the conductors.
All in all -- this means you'll be splicing in the base of your lamp, and putting some sort of extra insulation in the pipe to prevent wires from rubbing against the pipe. (If nothing else, a square or octagonal metal junction box would make a reasonable 'hub' for your lamp base. Just attach the black iron pipe as if it were conduit, and put a blank metal faceplate on it to serve as a bottom piece.) The extra insulation material will also get you compliance with 410.18(A):
(A) Exposed Conductive Parts. Exposed metal parts shall be grounded or insulated from ground and other conducting surfaces or be inaccessible to unqualified personnel. Lamp tie wires, mounting screws, clips, and decorative bands on glass at least 38mm (1 1/2 in.) from lamp terminals shall not be required to be grounded.
As to the FPN mentioning 110.14 (which is where the answer to your specific question is, the rest of this is for the next guy from Google who finds this post!), the relevant section is 110.14(B):
(B) Splices. Conductors shall be spliced or joined with splicing devices identified for the use or by brazing, welding, or soldering with a fusible metal or alloy. Soldered splices shall first be spliced or joined so as to be mechanically and electrically secure without solder and then be soldered. All splices and joints and the free ends of conductors shall be covered with an insulation equivalent to that of the conductors or with an insulating device identified for the purpose. (second paragraph of quote omitted as it is utterly irrelevant for this answer)
So, wirenuts or push-in connectors are the best idea here -- they're identified for the purpose (clearly!), provide their own insulating device, and are trivial to obtain.
What is considered proper 'extra insulation' within the pipe? Per "Protection of Conductors and Insulation. Part (B) Protection through Metal" @ThreePhaseEel Mar 16, 2017 at 0:03
@user782860 the classic is the old varnished-paper stuff, but a rated insulating sheet or tape around the wires (usually plastic) is a better idea... Mar 16, 2017 at 0:08