Looking to add a 20 amp receptacle on the outside of my house, on a separate circuit. I don't know what NEC codes to look out for. It will be on the outside wall of the house, if that helps. The code I am familiar with is using the correct gauge for a 20 amp circuit.

2

For an outdoor 20 ampere circuit, you'll need a

  • 20 ampere breaker, obviously.
  • Minimum 12 AWG conductors.
  • GFCI protection either via a breaker, standalone device, or receptacle.
  • Weather-resistant type receptacle.
  • A weatherproof in-use receptacle cover (identified as "extra-duty").

If the box is not in the wall, you'll also need

  • A weatherproof enclosure.
  • Wet location rated protection of the wires via conduit, rated cable sheath, or other approved raceway.
  • Does LFMC count as Wet location rated protection, the house is brick so the box won't be in a wall. – MDMoore313 Sep 8 '14 at 13:22
  • Liquidtight Flexible Metal Conduit (Type LFMC) can be used in a wet location. However, it cannot be used where subject to physical damage. If it would be in danger from a weed whacker, you might not want to use it. It shouldn't be a problem, but you'll also want to make sure it's not exposed to temperatures in excess of the rating (-30°C (-22°F) - 80°C (176°F)). – Tester101 Sep 8 '14 at 13:39
  • so, are we talking sch 80 PVC then? weed wacker damage is possible, though unlikely lol. – MDMoore313 Sep 8 '14 at 14:13
  • If you have LFMC laying around, I'd check with the local building department to see what they think. I can't see where you're installing it, so I can't say for sure from here. – Tester101 Sep 8 '14 at 14:19