I have a detached garage approximately 50' from the house supply panel. I want to wire 6 outlets & maybe 2 overhead lights. I will have no heavy use, mainly 1 outlet & overhead lights. I have installed underground conduit approximately 25' between house & garage but not below the frost line. The main panel is all 20 amp breakers, with 12-2 wiring.
Can I run standard 12-2 to the conduit, tie 12-2 underground through the conduit then retie to standard 12-2 to wire garage? The underground conduit is sealed Schedule 80 PVC.
  • When you state 12-2 that usually refers to NMB or romex and this would not be legal underground in conduit. This location would be listed as a wet location and NMB is not listed for wet locations. UF could be used but since there is conduit I would use dual rated wire like thhn/thwn. thwn is listed for wet locations and would be much easier to pull through conduit.
    Feb 8, 2019 at 18:14
If you're not planning on installing an electrical panel in the garage, the installation is quite straight forward. You can basically treat the garage circuit, just like any other branch circuit. If you do plan on installing a panel in the garage, the following information is not for you.
Overview
You'll install a 20 ampere breaker, in the panel in the house. From there you can either go straight into conduit, or you can run any other approved cable. From the question, it sounds like you want to use nonmetallic sheathed cable from the panel, which is just fine. You'll connect the 12/2 with ground NM cable appropriately in the panel, and run it out to a junction box near where the conduit will leave the house.
Then you'll run conduit from that junction box, outside, underground, then up and into the garage, ending at another junction box. You'll want to make sure you install expansion fittings where appropriate, especially if you're entering the buildings above ground.
Next you'll pull three, 12 AWG THWN wires through the conduit. Connect the wires from the NM cable, to the THWN conductors in the junction box in the house.
Finally, you'll run cable from the junction box to the outlets in the garage.
Single, or Multi-wire branch circuit
National Electrical Code allows a garage to be supplied by a single, or multi-wire branch circuit without much trouble. If you don't plan on using much power, and don't mind having the lights and receptacles on the same circuit. You can simply run a single circuit out to the garage, and power everything with it. However, if you want to separate the lighting load from the receptacles load, you can install a multi-wire branch circuit without much extra effort.
If you decide to install a multi-wire branch circuit, you'll have to install a double pole breaker instead of a single pole breaker. So to do this, you'll have to have two slots open in the panel. You'll also have to install an additional conductor, so you'll have to use 12/3 NM cable and pull and extra wire through the conduit.
Conduit Size
Whether you decide to install a single or multi-wire branch circuit, you'll need to use at least 1/2" conduit if you're using schedule 80 PVC. According to Table 5 of Chapter 9 of the National Electrical Code, each 12 AWG THWN conductor has an approximate area of 0.0133 in.². Table 4 of the same chapter, says that 1/2" schedule 80 PVC has a total internal area of 0.217 in.². However, since there are more than 2 wires in the conduit, you can only fill the conduit to 40%.
0.0133 in.² * 3 conductors = 0.0399 in.²
0.217 in.² * 0.40 = 0.0868 in.²
Three 12 AWG THWN conductors will take up 0.0399 in.², while 40% of the total internal area of 1/2" schedule 80 PVC is 0.0868 in.². So there's no problem fitting the 3 conductors through the conduit.
0.0133 in.² * 4 conductors = 0.0532 in.²
Even if you decide to run a multi-wire branch circuit, you'll still have plenty of room in the 1/2" conduit.
Conduit Minimum Cover
According to Table 300.5 of the National Electrical Code, direct burial nonmetallic raceways not encased in concrete or other raceways is required to have a minimum cover of 18" (450 mm). However, if it's a residential branch circuit, 120 volts or less, GFCI protected, with 20 ampere or less overcurrent protection, it can have a minimum cover of 12".
So if you're installing a single branch circuit to supply the garage, you can install a GFCI breaker and you'll only have to bury the conduit 12". Otherwise, you're going to have to bury the conduit 18".
NOTE: Minimum cover is based on the conduit running under nothing but grass and dirt. Minimum cover may vary if run under concrete, walkways, streets, parking lots, etc.
Grounding and Bonding
Since you'll only be installing a single or multi-wire branch circuit, you'll only be required to run an appropriately sized grounding conductor along with the current carrying conductors (250.32(A)Ex. 1). You'll extend this grounding conductor to each outlet, and connect any devices to it. There are no other grounding or bonding requirements, as long as there are no metallic pathways connecting the two structures.
Means of disconnect
As Speedy Petey points out, you'll also need a means of disconnect inside or outside the building near where the circuit enters (225.31, 225.32). A means of disconnect is simply any approved method of disconnecting all ungrounded conductors. This could be simple snap switches, a pullout disconnect, a safety switch, etc.
Outlets required
Once you supply a garage with electric power, you'll also have to install a few required outlets. First you'll need at least one receptacle outlet (210.52(G)(1)), which will have to be GFCI protected (210.8(A)(2)). You'll also have to install one switch controlled lighting outlet inside (210.70(A)(2)(a)), and one switch controlled lighting outlet on the outside to provide lighting for the entrance/exits (210.70(A)(2)(b)).
Single branch circuit supplying garage Single branch circuit supplying garage
Multi-wire branch circuit supplying garage Multi-wire branch circuit supplying garage
Notes:
  • This answer is based on National Electrical Code 2014, and may not be applicable to areas that do not follow NEC.
    Don't forget that a disconnect is required at a detached structure. A simple snap switch rated for the circuit is adequate, or even a "pullout" disconnect will work for a multi-wire circuit and is about the cheapest route. Sep 4, 2014 at 12:09
  • @SpeedyPetey Thanks. I always forget about the disconnecting means. I also added some info about the required outlets.
    – Tester101
    Sep 4, 2014 at 12:37
  • How do you find the time to present so much information - Awesome - i like the picture
    – Prasanna
    Sep 5, 2014 at 6:54
  • Is conduit typically required? My neighbor was telling me you can run just the wire itself in a 12" trench without conduit. This seemed dangerous. He was also trying to tell me that you couldn't lift up a garage door without a door opener though, so... Nov 5, 2016 at 4:38
    @JoePhilllips You don't have to use conduit, you can use a cable that's rated for direct burial. However, you'll have to bury the cable 24" deep, unless local amendments say otherwise. Also, you can open a garage door without the opener. As long as the springs are properly tensioned (or you're really strong), and you've pulled the release to disengage the lift trolley from the door.
    – Tester101