This situation suggests that the neutral conductor has a problem somewhere between the dryer outlet and the panel.
The conductor should behave as a very low resistance, which drops 0V (in particular in a multimeter test, where very little current is permitted to flow due to the very high resistance of the meter).
Of course, the voltage between the neutral point at your panel and either of the hot wires is 115. But, only 40V of that is being dropped by your meter: the other 75 is dropped by the neutral wire. Your meter's resistance is forming a 40:75 voltage divider with the neutral wire's resistance. And since your meter's resistance is very high (probably 10 million ohms or more), it means that the wire's resistance is on the same order: it is close to twice the resistance of your meter (40:75 is almost 40:80 or 1:2).
In practical terms, it means that the neutral connection is broken somewhere. Perhaps the wire itself is broken, or a hookup. Even though the connection is broken, current is able to find a way to flow through an alternative path, which has a very high resistance. This current shows up as a voltage of around 75V which subtracts from 115 to leave 40 across your meter. The voltage is simply from Ohm's Law: V = IR. Some tiny current I, flowing through a huge resistance R, happens to make 75.
Example with diagram:

Here, the multimeter is symbolized as a 10 megohm resistor. The bad neutral wire is modeled as a 20 megohm resistance. This means that AC voltage between point A and B (what the multimeter measures!) will be 115 x (10/(10 + 20)) = 38.3V. If the neutral connection weren't faulty, the meter would take the full voltage and show 115. This is all exactly same if we disconnect the meter from point B and connect it to point C instead: the other AC phase. Between the two phases, there is no fault: if we measure between B and C, we get 230 because they are opposite phase, and since ground isn't faulty, then from ground (such as point D) to ether B or C, there is 115 VAC.
The resistances are just representative. Your meter and the faulty connection could both have a much higher resistance.
A final point is that the voltage measured in a circuit where there is a high impedance is real, but the specific value is not meaningful. That specific voltage value only exists while the meter is connected to the circuit. Another multimeter could read very different value. The multimeter is designed under the assumption that the resistances in the circuit which it measures are small compared to that of the multimeter, so that the multimeter's resistance dosn't disturb the voltages in the circuit.
{}