21

Is it worth the time and expense to put the foam pipe wrap on pex hot water pipes? I've seen mixed statements.

What is your thought? But more importantly, can you back it up?

2
  • Are you thinking of hot water supply for things like showers? Or HW piping used for space heating purposes? Commented Jan 1, 2019 at 23:35
  • 1
    @DaveInCaz The original question was in respect to hot water supply, however even for space heating you would probably want to insulate, so that you can add heat in the specific location that you want.
    – Dilbert789
    Commented Jan 15, 2019 at 16:08

17 Answers 17

14

It's definitely worth it if you are running new pipes or the existing pipes are easily accessible, but if you have to lift boards etc. to gain access probably not.

PEX is a very good conductor. One of it's uses is for under floor heating systems, so if you are using it for delivering hot water the it's definitely worth insulating it. This is true of copper pipe as well.

3
  • 2
    For a water usage POV, if you kitchen, and bathrooms are at all connected. you will find that when you sporadically use any faucet, you can still make use of the warm/hot water in the pipes (with insulation), my bathroom requires me to run the water for about 30s before it gets warm, then if i try again in about 5 mins, i need to run it for 30s again. -- waste of water and electricity.
    – Hightower
    Commented Jan 9, 2015 at 7:41
  • 1
    PEX is used for radiant floor heating and for radiant heating to de-ice driveways. Which means it is a very good thermal conductor. So there is definitely a benefit to insulating it, because it has no significant insulating properties of its own. Commented Jan 16, 2015 at 4:15
  • Pex has about 2% the thermal conductivity of water.
    – isherwood
    Commented Feb 1, 2017 at 17:56
12

Maguire, Fang, and Krarti have developed a simulation model to estimate the energy losses for prototypical domestic hot-water distribution systems. As an example application of their model, they assessed the impact of insulating pipes in unconditioned space (Figure 12):

Figure 12

When they combined this with estimates for the cost of insulating the pipes, they found that “In the most cost effective case of adding ½ in. (12.7 mm) insulation to the distribution system of a high use home in Atlanta, the simple payback is estimated to be 26 years. Adding insulation to just the section of piping in unconditioned space appeared much more cost effective, with simple paybacks less than 10 years possible for homes in colder climates.”

Note: This paper assumes the price of 3/4" insulation to be $3.30/ft. 1" insulation can be had for about $0.45/ft currently (Jan 2021), about 7x cheaper, thus reducing the payback period drastically.

These results were all with copper pipes. Another report quantifies the heat loss from copper pipes and PAX pipes (a 3-layer composite of high density cross-linked polyethylene (PEX), aluminum, and another layer of PEX) but not for straight PEX. They note, however, that “½ inch thick foam pipe insulation performs almost as well as ¾ inch thick foam pipe insulation.”

3
  • Wow I would think it would pay back faster, possibly if they added broken due to freezing it would pay back much faster with copper but pex expands and is ok after a freeze or so far it has been. You have the data should be the approved answer since data was requested.
    – Ed Beal
    Commented Jan 24, 2018 at 23:22
  • @EdBeal insulation might delay damage from freezing but wouldn't prevent it in many cases. But I guess statistically that could improve the payback. Commented Jan 1, 2019 at 23:34
  • 1
    I have seen pex at close to 3x it's normal size frozen solid. Copper is my choice for plumbing but even it has problems with some water systems, I have not seen apex burst and maybe I am to old school trained to cut and thread galvanized then moved to copper for general construction. Some of the biggest profit repairs my dad's business handled were ones they chose particle board and PVC pipe , now I prefer. Copper because it is awesome and can take some freezing but have seen pex literary split studs and not break but I woorry about the life span it's plastic so that is my concern.
    – Ed Beal
    Commented Jan 2, 2019 at 4:19
8

There are two reasons to insulate hot pex pipes:

  1. Keep them hot in cold temperatures
  2. Keep them from heating up cold pex pipes

When we ran our pex, we were very careful to keep the hot and cold pipes from touching, so #2 wasn't an issue. In my climate, I was more concerned with keeping the cold pipes from freezing and insulated them, particularly where they were near the exterior of the house or where they crossed near a cold air intake/vent.

1
  • ConsultUtah - how have your PEX pipes fared in really cold weather? I live in an area where there are frequent power outages so I'm looking for the best passive option (probably PEX-A + insulation) to handle sub-zero temps.
    – elPastor
    Commented Aug 29, 2019 at 15:52
6

Yes, I'd insulate: not least because the water in the pipe will stay warmer longer. Although PEX is a better insulator than copper, having hotter water come through the pipe faster is a good thing.

2

The PO did it in my house, but we have a well. He insulated the cold-water pex wherever he could, probably because it sits in a pressure tank and he was hoping it would stay cold.

When you touch the cold and hot copper, you can feel cold and hot which means the heat transfer for copper tubing is efficient. (should insulate)

Grab your pex and see what you can feel.

5
  • The hot water pipe is quite warm. If the water runs for a bit the piping heats up to the temperature of the water though.
    – Dilbert789
    Commented Jul 26, 2010 at 12:41
  • Adding insulation then would definitely help. I am not sure how long it would take you to recoup your investment. I would only think about it if you are running the pex through a cold area, and you live in a colder climate. Commented Jul 26, 2010 at 20:29
  • 6
    Actually - the opposite. If you can feel hot or cold through the pipe then it is an efficient /conductor/ of heat, not an insulator at all: it's conducting heat to your fingers! Commented Jul 30, 2010 at 19:09
  • 2
    If you're in a humid climate, it's good to insulate the cold pipes to prevent condensation, which will eventually start dripping onto whatever is below the pipes.
    – gregmac
    Commented Jul 31, 2010 at 6:30
  • 6
    Jeremy: That's actually what I wrote. The heat transfer is efficient, not the insulation. Commented Oct 12, 2011 at 19:31
2

It depends where the pipes are, if within a well insulated house, the return in efficiencies will not be that great. But if it is in an area where extereme cold could come (under the eaves, or in the loft) normal loft insulation will not be enough. So if you can get (like this year in Europe) a long term cold spell of -10°c to -20°c - pipe covering insulation (the grey foam type) is well worth it with regards to stopping freezing.

2
  • Preventing freeze is not a good reason to insulate the hot water pipes. If you have frozen pipes issues, insulating only the hot one will not help much.
    – Jeffrey
    Commented Jan 24, 2018 at 15:04
  • Insulating pipes, even in a conditioned space, definitely helps. My pipes are in my basement, which it's consistently about 10 deg cooler than the house. Insulating the cold line stopped condensation & dripping on the floor & contents. Insulating the hot line cut the time & wasted water to get hot water at a fixture by at least half. It also raised the hot water temp at the fixtures, allowing me to turn down the water heater temp for further savings. Commented Nov 27, 2019 at 15:10
2

Any insulation will prevent heat from transferring out of hot water pipes or into cold water pipes. There are several considerations:

  1. Cost of insulation
  2. Cost of labor to install insulation
  3. Heat conductivity of tubing (copper transfers heat more than PEX tubing)
  4. Amount of water that must be run through the piping to get hot or cold water at the faucet

    a. Cost of unused heated water that goes down the drain (both water charges and heating charges) b. Cost of sewer charges for that water

You may want to consider a circuit setter (like Circuit Solver) with a hot water return line so that hot water circulates (does not run to drain). The result will be that hot water is more quickly available. However, the circulation speeds up heat transfer out of the pipe, so insulating is still desirable.

2
  • Any insulation will reduce heat from transferring out of hot water pipes or into cold water pipes. The question is how much reduction and its value. Commented Mar 1, 2013 at 19:30
  • One potential way to reduce the insulation cost is using pool noodles instead of pipe insulation. In my area I can get noodles from a dollar store for $1 per 4ft, ($0.25/ft) while thinner pipe insulation costs about $3.50 per 10ft ($0.35/ft). The noodles also come in different colors. I used red for hot water, blue for cold, and may use orange if I add a hot water recirc system. Commented Nov 27, 2019 at 15:17
2

Check out the link to Nomaco Insluation: http://www.nomacoinsulation.com/pdf/polyolefin%20faq/TA65%200512.pdf

Basically, the r-value of PEX insulation does not meet energy code requirements for piping insulation.

Also, according to ASHRAE Research (2015 HVAC Applications, page 50.4): "Table 1 also shows that all of the plastic pipes tested to date exhibit moderately to significantly higher heat loss rates than comparably sized copper pipes when tested uninsulated in air. However, when insulated, they exhibit moderately to significantly lower heat loss rates than comparably sized copper pipes with the same insulation."

So, I think you would be silly not to insulate PEX piping.

1

I really doubt it is worth it and I have never seen it done.

1

Do the PEX feel warm to the touch? If so, you're losing heat, and thus would benefit from insulation.

The cost of pipe insulation is negligible, and it lasts for decades, so the cost/value is skewed in favor of insulating.

1

The cost benefit is very difficult to accurately calculate. The convience of having a hot water pipe charged with hot water while several people are in the house, washing hands, washing dishes, taking showers, combined with having hotter water to work with, is the biggest reason to insulate hot water pipes. I used 4 inch diameter fiberglass around my 3/4 inch copper main line. That gives me 1.5 inches of thermal conduction resistance. The water stays warm in the winter for about an hour. It stays hot for fifteen minutes. Without the insulation the water cooled in five minutes.

1

Yes it is good to insulate the lines, as mentioned before, if the Cold water runs in unconditioned space or your condition space is kept at a higher humidity level.

For Domestic Hot water many newer codes are requiring a Hot Water return (on demand) circulation along with 1/2" insulation on 1/2" piping. After 1/2" the benefits will depend on the particular setup and routing of the piping.

0

Probably not worth it.

Considering how much the insulation costs (not to mention install costs though this is diy so that should be $0) I think it would take a long time to make up for the cost of water that goes down the drain to get to the hotter water from the tank and well as the cost to heat that extra water to a temperature that the insulated pipe water would have been.

I would need (or technically, that guy from XKCD would need):

  1. water costs in your area
  2. Length and diameter of the pex from the tank to an average faucet
  3. average temperatures inside and outside your house and
  4. the percentage of the pex that is inside your house
0

I have insulated my PEX tubing and found that it does make a difference. My master bedroom is over my garage (unconditioned space) and the tubing runs through knee walls (unconditioned space). This is the only room we heat with oil. The rest of the house we heat with wood pellets. But ever since I insulated the tubing the boiler does not run as much. So yes, I would insulate.

1
  • this is very unclear. is your pex carrying water for drinking and washing or water for heating? it makes a difference. Commented Mar 1, 2013 at 19:31
0

Here is an unusual use for the insulation. At a commercial building they had chunks of insulation all over the PEX, hot and cold. They had the PEX secured all over, though they had the insulation between the places it was secured. They said the reason was to prevent the PEX from vibrating the studs they were attached to.

0

It just makes sense to spend a few dollars to ensure your hot and cold water PEX pipes are well insulated for energy consumption if no other reason, but with the winters we have been experiencing here in the northeast during the last few years, it pays to do what you can so the pipes don't freeze. I used the fiberglass tubing on the hot water lines and the foam tubing on the cold on the advice of a plumber.

0

Yes! I want hot water when I turn it on, not 15-30 seconds later. The extra $100 bucks, I don’t care if I make it back in energy savings. The convenience alone for me is the payoff.

1
  • Hello, and welcome to Home Improvement. Thanks for the answer, but note that this will only work for some tens of minutes after someone uses the hot water; after that, no matter how much insulation you have, the water will be cold. And, you should probably take our tour so you'll know how best to contribute here. Commented Nov 26, 2019 at 20:35

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.