Currently designing a 2500sqft house in the Sierra Nevada mountains at 6300ft elevation. It's an A-frame with a loft and living room area has high 20ft ceiling peak. It snows 4 months of the year, and summers are moderate with one or two 90˚ days. So I'm going to forego cooling, but considering options for primary heating:
Electric Radiant flooring: I was planning to use this for bathrooms under tile anyway, but why not just extend to the whole house? I drew up a plan to lay about 820sqft of resistance wire mats through out the house totaling 10kW of power. I estimate the total cost would come out to $12k installed.
Traditional Forced Air Central System: No access to gas, so this would be electric too, probably sized around 3 Ton, which would be around 10.5kW. This will certainly cost me in the $20k range installed.
Heat pump system: I was advised heat pumps would not perform well at this elevation and climate where temps go below freezing for a significant part of the year.
I'm drawn to the electric radiant heat idea. It seems more efficient because of direct heat delivery as opposed to duct losses with a forced air system. I'd also be able to have multiple zones individually controllable. QuiteWarmth system
In the above described scenario, are there any other pros/cons to consider? Or suggestions on other energy or cost-efficient heating sources where natural gas is not available?
Edit 1: More specific question to make this less open-ended. Here's an electric radiant floor mat layout plan I drew up for the living floor, which is about 1800sqft. Is 9.8kW worth of heating enough for this area?
Edit 2: Thanks for all the great answers and comments. Did a ton of research to get ball park numbers into a spreadsheet to understand how much it will cost and what is the breakeven point vs plain electric.
Two critical inputs are the heat pump efficiency at different temperatures. I looked through the manual of a 28kBTU copper+hunter unit and pulled out some COP figures that seemed reasonable. But it provided for heating:
- COP @ 47F outside ~ 3.7
- Rated capacity at 17F ~ 17kBTU
- Max capacity at 5F = 21kBTU
Question 1: Why would the max capacity be higher at 5F compared to rated capacity at 17F? What is the difference between rated and max capacity?
Question 2: I assumed COP @ 47F is 3.5 and COP @ 17F is 1.5. Are these reasonable estimates?
Question 3: Very hard to find COP vs outside temp charts for most available units, so what average figure can I assume for COP @ 5C for example?
Question 4: Finding that it will take roughly 4-7 years to breakeven on the investment required for either heat pump or propane. Is this what one might expect vs going purely electric, or am I being too optimistic here with incorrect assumptions?