I have installed a 200 amp distribution panel w/socket head. Will this be considered my main panel, and my panel inside now becomes my subpanel?
Should my subpanel be unbonded, and 2 lines, 1 neutral, plus ground be provided to the subpanel?
I have installed a 200 amp distribution panel w/socket head. Will this be considered my main panel, and my panel inside now becomes my subpanel?
Should my subpanel be unbonded, and 2 lines, 1 neutral, plus ground be provided to the subpanel?
If the new meter panel is feeding the old panel, the old panel is now a subpanel of the new panel, which becomes the main. The subpanel should not bond neutral to ground, but the main panel should.
On what "loads" are located in the outdoor panel. If no loads are there, then NEC 230.85 lets you pick and choose which one is the "main panel" for grounding/bonding and neutral separation purposes. You must label both breakers with specfic markings depending on your choice.
If there are loads in the outdoor panel, then it greatly depends which loads they are. NEC 230.82 has a list of loads which are allowed on the service side of the main breaker, and those (only) can be in the outside panel while still calling the inside panel the "main panel". That includes things like
If there are loads in the outer panel not subject to a 230.82 exception, then the outer panel is the main breaker and the feeder to the original panel must be 4-wire (retrofitting ground allowed, see 250.130(C).)