Yet another GFCI tripping post. My issue is that I have a new installed 20A GFCI receptacle that is tripping as soon as I turn the breaker on without a load attached. I've done everything I can think of to test what is going wrong with this and I am at a loss. Since I know you'll ask, I have:
- Wired LINE to the panel (Brass to hot/black, Silver to neutral/white, Bare wire to ground screw)
- Left LOAD unconnected.
- Checked with a multimeter for resistance between hot-neutral(O.L), hot-ground(O.L), neutral-ground(0.1 ohm)
- Checked with a multimeter for voltage between hot-neutral (123VAC) and hot-ground(123VAC), neutral-ground(0VAC)
Besides this thing tripping without a load connected, I'm also not sure about neutral to ground continuity. I've read that neutral to ground can cause a GFCI to trip... but I've also read that they are supposed to be tied together in the panel to maintain the return path... So I'm confused.
This is the second new GFCI I've tried in the past 2 days - thinking that it was a faulty GFCI. There are other GFCIs in my house that work just fine - and I cannot tell what the difference is in the panel wiring between those GFCIs and the one I'm currently installing.
Here are the things I've "read" as far as GFCI tripping causes and the neutral-ground bonding in the main panel:
Why is the neutral tied to ground in my home's electrical panel?
Why would bridging Neutral and Ground trip a GFCI breaker?
The romex from the GFCI to the panel is easily traceable, and I've included some pictures below of the GFCI wiring and the panel wiring, as well as the wiring of the GFCIs that are working fine.
Overall my question(s) is: Why is my GFCI tripping without a load attached? Does this have to do with the neutral/ground bonded at the main panel? Why do the other GFCIs work fine and not the one I am installing? Is there something else I should check to provide more information or troubleshoot this?
Thanks for any feedback.
UPDATES
Yes, I did press the reset button after supplying power to the GFCI. Plugs still do not have power and the reset switch stays red.
The receptacle is the Eaton GF20W.
The box I am using is plastic. No metal inside.
Solution
I swapped out the Eaton brand as per @Robert Chapins suggestion for a different brand of the exact same product (Leviton) and that worked. I have no idea why, but it works.
Picture of the back of the GFCI causing issues.
Picture of the front of the GFCI causing issues.
Picture of the breaker that the GFCI is connected to. It's the one that is flipped off.
Overview of the panel wiring with the two working GFCIs marked with red boxes, and the problem GFCI marked in another red box (sorry for fuzzy text).
Picture of one of the breakers that has a working GFCI receptacle.
Picture of another breaker with a working outdoor GFCI.