I am planning on running an electrical service (240V, 100A) from house to a detached garage.
I am looking for feedback on my plan.
Site:
- Western New York State
- Main House Panel is at the furthest location from the detached garage in an unfinished basement (poured concrete floor and open floor joists)
- Detached garage has an existing 200amp panel
- Pool is an obstacle on the backyard side of the house
- Driveway is an obstacle on the front yard side of the house
- Garage on the opposite side of main house panel (no basement under garage)
- Basement length: 86 feet
- Basement exit to trench entry on side closest to house: 48 feet
- House to detached garage: 100 feet
- Total run: 234 feet (for discussion lets say 250 feet)
Plan:
- Use 2/0 AWG Al THHN/THWN-2 wires for hots and neutral
- Use 6 AWG Al THHN/THWN-2 wire for dedicated ground back to panel (?1)
- Run wires from the Main House Panel in a 2" PVC 40 Sch conduit, in the basement (86 feet), surface mount on side of exposed foundation (48 feet), and in a 24" trench (100 feet) to the detached garage (?2)
- Main house panel breaker will be 100 Amp
- Two grounding rods from detached garage sub panel 6 feet apart with 6 AWG Cu wire (?3)
Question 1: Ground wire size appropriate? Naked ground permissible?
Question 2: Does the basement run need to be in a conduit if using wires instead of a cable? Can the trench run be another wire type, like USE-2? Are junctions between wire types in run lengths like mine common and advisable? Any issues with running PVC conduit surface mounted on exposed foundation?
Question 3: Does this have to be a naked wire?
In general I appreciate any feedback and my main concern is the need to run 2" conduit inside the basement as I would like to avoid it if possible, both for space and cost savings. However, I am worried about splices between different cable types.
Any other advice or recommendations would be welcomed as well.