I remodeled my kitchen installing larger/deeper sink and a new disposal. I am wondering if the installation meets the code in terms of the height difference between the disposal and the drain outlet at the wall. Shown is a picture of the new drain- just a dry fit for now. Is it ok to go ahead and complete the installation?

enter image description here

3
  • You need to provide your jurisdiction to determine whether it meets code. Looks good to me, though.
    – Matthew
    Commented Apr 1 at 19:14
  • MA state, is there any specs on the min height between the end points ?
    – hrs
    Commented Apr 1 at 19:17
  • That's a disposal, not an "aerator". Aerators are on the ends of faucets. You might be thinking of "Insinkerator", a manufacturer.
    – isherwood
    Commented Apr 1 at 19:33

1 Answer 1

2

You really have just two key dimensions to worry about, assuming appropriate pipe size and slope (which you seem to have). They are maximum tailpiece (disposal output pipe) height and maximum trap arm length. You're fine with both by a good margin, assuming a vent stack shortly inside the wall. It all looks dandy.