3

Saw a picture of an example of code NEC 300.4 (D) where a furring strip was used and a wire was run parallel to the furring strip. Per the code, the wire was 1 1/4" away from the nearest edge of the furring strip.

enter image description here

This doesn't make sense since the wire has the same chance of getting hit with a nail if the wire was only 1/2" from the furring strip. I realize that this originated from the fact that a hole in a stud has to be 1 1/4" away from the top facing edge of a stud to keep drywall screws from hitting the wire.

But according to this code a wire can be just under the sheetrock as long as it is 1 1/4 " away from the furring strip. I don't understand the logic. Can you please clear up my confusion?

National Electrical Code 2011

ARTICLE 300 Wiring Methods

300.4 Protection Against Physical Damage. Where subject to physical damage, conductors, raceways, and cables shall be protected.

(D) Cables and Raceways Parallel to Framing Members and Furring Strips. In both exposed and concealed locations, where a cable- or raceway-type wiring method is installed parallel to framing members, such as joists, rafters, or studs, or is installed parallel to furring strips, the cable or raceway shall be installed and supported so that the nearest outside surface of the cable or raceway is not less than 32 mm (11⁄4 in.) from the nearest edge of the framing member or furring strips where nails or screws are likely to penetrate. Where this distance cannot be maintained, the cable or raceway shall be protected from penetration by nails or screws by a steel plate, sleeve, or equivalent at least 1.6 mm (1⁄16 in.) thick.

1
  • Please don't make radical changes to your questions like that, especially after someone has gone to the trouble of answering the original version. Ask a new question instead.
    – Niall C.
    Commented Jul 15, 2013 at 21:25

1 Answer 1

2

I’m not a NEC attorney nor did I stay in that fancy motel last night but one of the “intents” of “the rules” is to reduce the number of material casualties suffered during construction. A sheetrock craftsman won’t use 16-penny nails to mount sheetrock and is highly unlikely to miss the studs or furring strip with a standard drywall nail or screw, hence the 1 1/4” (and metal plates) rules. Mr. Homeowner, while installing a shelving unit for knickknacks might use a 16-penny nail but I’m confident wiring a house with EMT would turn expensive in a hurry.

11
  • Ouch. Changing your question makes my answer look like I've been hittin' the bottle. (grin) Where did you see that 14awg rule and why would 14awg differ from 12awg? The intent is to prevent standard mounting devices (nails and screws) from breaching the insulation, 1 1/4" deemed a safe distance under "normal" or "typical" installations. Commented Jul 15, 2013 at 21:25
  • @JoeFromOzarks Changing the question like that is considered bad form on this site; I've rolled it back and asked the OP to open a new question.
    – Niall C.
    Commented Jul 15, 2013 at 21:30
  • Sorry, Niall. Thanks for rolling it back. @JoeFromOzarks Thanks for your reply. I used 14 AWG; should apply to other common wire.
    – BobJax
    Commented Jul 15, 2013 at 22:31
  • Seems like the solution is to state that if wiring is placed where furring strips are used, the furring strip must be thick enough that wiring can be placed under the furring strip (attached to the wall) and be 1 1/4" from the top edge of the wood. When wiring is parallel to the furring strip, the furring strip must thick enough so that the wiring can be attached 1 1/4" from the top facing edge of the wood. Basically 3/4" thick furring strips would have to be doubled. When asked how the illustrator of the picture came up with his interpretation, there was no answer (that I could find).
    – BobJax
    Commented Jul 17, 2013 at 13:14
  • If you’re taking the exam, all the information you need is in the text and pictures. For an apartment where risk is slight, you can follow the NEC and probably be fine, forever. However, building a wall for a fellow’s machine shop in his personal garage, I’d be recommending EMT for ensured (additional) protection. :) Commented Jul 17, 2013 at 13:35

Your Answer