An animal shelter (in USA) where I volunteer has a new 240V Maytag electric dryer that will not operate (when "on" is pressed, the electronic panel gives a single brief flash of all LED's, that's all). The Maytag service tech says the power is defective because he measures 163V from hot leg to ground; he expects 120V (as one finds in residential split-phase 240V) and says the problem is in the power wiring, not the machine. We have no other power source to try.
The dryer has a three terminal panel with two hots and a ground (no independent neutral), to which a NEMA 10-30 cord/plug is attached and correctly wired. It is plugged into a NEMA 10-30 receptacle, also correctly wired. The voltages at the receptacle and inside the dryer are 240 hot to hot, and 163 from either hot to ground. The building is commercial and has three-phase service.
I think all this is as it should be, given that the building has 3-phase service and no neutral is employed, and the problem is in the dryer. Am I correct, or have I missed something? (I'm not looking for an explanation of three-phase delta/Y or center-tapped transformers, just whether the power wiring to the receptacle is correct and the voltages normal.)