I have a 12 year old Pottington gas combi-boiler running my radiators and water tank. I was checking the central heating loop pressure today and I discovered a twisty valve I never used before. I think this valve has been incorrectly set since I bought the house, and it appears to connect the boiler water OUT to the boiler water IN, short circuiting the radiators. It is a smaller pipe than the main one. It is located beside the boiler.
- The radiators don't heat up very quickly, I had assumed it was just because the weather was extra cold
- The boiler powers down every few minutes, including soon after a cold start
Please see the diagram below.
- I found the valve fully open (anticlockwise) and it was stiff, not recently turned.
- I measured temperatures, see diagram:
- 47°C
- 27°C
- 47°C
In this configuration the water seems to be going through the short circuit and so the boiler turns off soon. The radiators still work and have done for 6+ years but they could heat more quickly.
Turned the value to fully closed (clockwise), and now
- measured temperatures:
- 47°C
- 33°C
- 33°C
- boiler ran much longer even when the thermostat dial was turned down
So these are my conclusions:
This valve allows a significant amount of hot water to short-circuit into the return from the radiators, limited by the smaller diameter of the pipe. The boiler thus receives a warmer return water and cycles off quite quickly, limiting the speed at which the system can heat. Is this good for the boiler?
And my questions are this:
- What is the purpose of this valve?
- Should it have been fully open?
- Where should it normally be placed and why?
- Will it do any damage to place it fully closed?