The air handler for my heat pump has supplemental electrical heating. Currently it seems to be fed by aluminum wire, I think a service line bundle of 1/0 gauge. The breaker is 240V, 125 amps.
If I'm reading the electrical information label on the unit, however, it seems I'd need to size the wire for 85 amps and the breaker should be no more than 90 amps. There's only two hot wires running to the unit, so I assume it is in the "Single" section with just L1/L2. So the aluminum wire is correctly sized, but not the breaker. I'm thinking the 125 amp breaker was just what someone had in their truck on the install day...
Am I reading this label correctly? Are there any other considerations, such as any power the unit needs for the blower or is that already included in the label? There are no other electrical lines from my load center running to the air handler, and no boxes, breakers, fuses, or anything in between.