I have a ~20 years old Weil-McLain Gold oil boiler connected to the forced hot water baseboard heating system in a 2-story house (two zones with separate pumps, one for every floor). The same heater is also used to heat up tap water.

Recently, the hydronic part started to work very inefficiently: it was kinda able to maintain the temperature, but only by running without stopping for hours (instead of usual minutes). The return pipes were absolutely cold to the touch, and it was heating up only about 20 feet or so of the pipe along the baseboard. The tap water part was and is OK.

Upon investigation, I noticed that the pressure in the system dropped to about 5 PSI (which seems to correspond very roughly to the pressure of 10 feet of water, that is the elevation of the second floor baseboard). This figure comes from a built-in pressure gauge in the heater.

The system has an autofill valve (Watts TB1156F), which is supposed to be set to 15 PSI.

I turned off the boiler and opened the drain valve which is located on the return pipe close to the boiler. All the water had drained out, and the pressure dropped to zero, but the autofill didn't kick in.

The valve has a lever connected to a rod that you can push to temporarily turn off the valve pressure regulating mechanism and directly connect the heating circuit to the water main. When I pushed that lever, the system filled up very fast, and water (almost black, with a lot of sediment in it) started flowing out of the drain valve.

I waited until the water coming out of the drain valve became clear, then closed the drain valve and refilled the system by pushing the lever. It filled up unexpectedly fast and tripped the safety pressure release valve (set to 30 PSI). Next time, I was really careful with the lever and filled up the system to 15 PSI.

There are no bleeding valves on the baseboard pipes (or maybe I could not find them) There is a thing that looks like it might be a bleeding valve on the pipe downstairs, and also there is a thing which (I think) is an automatic bleeding valve on the top of the boiler. It has a tire-style stem protruding out of it, covered with a threaded cap with holes in it. When I unscrewed the cap, some air went out, then it started weeping water, maybe one drop every 15-20 seconds. The valve is covered in limestone deposit, which suggests that it is used to being exposed to water drying on it. I left it unscrewed just a little bit.

Over the next couple of days, the pressure dropped to ~7-8 PSI and the system became inefficient again. I downloaded the manual for the autofill valve and noticed that it had a screw to adjust the pressure. As I turned the screw just a smidge (maybe 15-20 degrees) clockwise, which is supposed to increase the pressure threshold, I heard the noise of water inside the valve and the system filled up to ~20 PSI.

This was yesterday morning, and during the day the pressure was steady (rising to ~23 PSI when the boiler was working and dropping to ~20 PSI as it cooled down). However, overnight the pressure has dropped to ~12 PSI and it looks like it keeps dropping.

I'm almost sure that the valve is broken and needs to be replaced, yet I have several questions:

  1. Is my understanding right and the autofill valve has failed indeed?
  2. Is it normal that the pressure is dropping during the normal course of operation? I looked closely but didn't find any leaks under the pipes, and most of them are not inside the walls (except maybe half-foot of each wall as it goes from room to room; and about 10 feet of the pipe hidden inside the concrete slab as it leaves the boiler). How can I test for leaks more reliably?
  3. Is the "automatic bleeding valve" I'm describing indeed that? If yes, should I leave its cap open?
  4. According to the manual, the autofill valve is supposed to be serviceable, and Watts even used to sell repair kits for it (although they have been discontinued). A new valve like this is around $80. Is it feasible or worth it to buy a new valve and replace just the mechanism by putting it into the old casing (to save on the plumbing labor costs)? Is it a DIY job?

Images (clickable)

  1. Autofill valve

    Autofill valve

  2. Automatic bleeding valve (?):

    "Automatic bleeding valve" (or maybe not)

  3. Expansion tank (top and bottom temperatures)

    Expansion tank (top) Expansion tank (bottom)

  4. Taco 241 check valve (?) on the return pipe downstairs, closer to the boiler

    Taco 241 check valve (?)

  5. Bleeding valve (?) on the return pipe downstairs, farther from the boiler.

    Bleeding valve (?)

3
  • 1
    You're asking too many questions here to get good feedback on any of them. Take the tour to find out more about the narrow focus expectations for Questions; then you can edit this Question to ask just one (and ask the rest in a separate Question). Jan 2 at 21:03
  • I suggest you add photos. Click Edit on your question, then use the mountains icon to add as many photos as needed. You've likely misidentified your expansion tank, which has failed and must be replaced, but to be certain, we have to see it. A view of the "auto-fill" (actually the pressure regulator) will let us say if it's easy to fix or replace. And so on.
    – MTA
    Jan 2 at 21:54
  • #5 is a gate valve. Neither air nor water should come out of that.
    – Ecnerwal
    Jan 3 at 0:40

1 Answer 1

1

Your core problem is not the autofill valve. The core problem is the leak (or leaks) in the system.

One of those leaks may be the automatic vent valve, which should only vent air, not water.

By flushing the old water out and refilling with new water, you've somewhat complicated short-term diagnosis because the new water came with new dissolved air, which needs to be removed from the system, and will cause more corrosion until all the oxygen in it is gone, either out the vent or by making new black (and/or orange, but the black is typical) corrosion from the cast iron and steel components exposed to it. Pressure will drop some from that process, and then some (smaller, if you don't flush any) amount of water needs to be added to replace it, then the smaller amount of new air needs to be removed...

So yes, you can replace the autofill valve, but that will just mean the leak continues, and new water is constantly added, and eventually the corrosion from the oxygen that comes in with the constantly-added new water makes a hole, plugs the pumps, or both. The choice to use cast iron and steel components in this service is predicated on there not being leaks, for long term part survival.

A non-leaking system should just vary between the "cold" and "hot" pressures, even with the water input to the boiler loop completely shut off. If pressure is constantly dropping, there's a leak.

6
  • Is there a way to isolate the leak if it's in the baseboard pipes? I've checked under the baseboards several times, there is nothing immediately visible.
    – Shivering
    Jan 2 at 22:15
  • That would depend on the valves on your particular system, (what sections of pipe can be isolated) and would require shutting the heat off in the isolated section, and any connected via it. With a 2-floor 2-zone system there may or may not be sufficient valves to isolate each floor from the system so you'd at least have heat in the other part of the house.
    – Ecnerwal
    Jan 2 at 22:22
  • Or the leak may be in the underfloor piping (quite common) or inside the boiler itself, where it turns to steam and goes out the exhaust pipe, at least until it gets big enough to make a puddle beyond what will boil off when the flame lights.
    – Ecnerwal
    Jan 2 at 22:59
  • Could you please look at the images and tell if I identified the parts correctly? The valve with the cap, should the cap be open or closed?
    – Shivering
    Jan 3 at 0:29
  • As for the valves: I think I can isolate the boiler itself (if I turn off the water main), the concrete part of the pipe, the exposed pipes downstairs and the pipes upstairs. How do I go about checking for leaks? Do I pressurize the pipes and see if the pressure drops over time? How much time should it take? (Please let me know if it's better asked as a separate question). Thanks!
    – Shivering
    Jan 3 at 0:34