I'm running a feeder to a 100A sub-panel. The total run is about 90 feet. 60 feet is in an attic, and I'm planning to use Aluminum SER 1-1-1-3, the other 30 feet is through a 1.5" PVC conduit on the outside of the house. I was planning to use THHN-2 or XHHW-2 Aluminum 1AWG conductors and a 6AWG Aluminum for ground. I'm planning to transition from SER in a large (10x10x4) box using Polaris lugs. Any issues with using a 6 AWG Aluminum ground?
Why does the Aluminum 1-1-1-3 SER have a 3AWG ground if 6AWG is sufficient?
I'm also running a Aluminum 2AWG bonding conductor through the same conduit, all the way from my main panel to where my main water pipe enters the house (within 3 feet of where it enters the house). My sub-panel is 10 ft away from where the water pipe will be bonded. Can I just run the 2AWG bonding conductor continuously from the main panel to the water pipe to the sub-panel and eliminate the Aluminum 6AWG ground conductor?