For a small brick ranch, two windows (24” and 28”) were added to a load bearing wall. 2x4 header was used over jack studs. However, the header is laying flat rather than on edge. I know having the 2x4 header on edge is superior but for two small window openings, would it be overkill to rip everything out and redo it?

I cannot find any uniform code reference for 2x4 header orientation. One other thing to note, header is directly under top plate if that matters.

It is a single plate, but the room is a converted carport, I just found a 2x8 beam running above the top plate so the wall, while exterior, seems to not be load bearing.

Essentially, previous homeowner had the carport closed in sometime in the 80s.

enter image description here

2
  • How does a 2x8 determine if the wall is load bearing? Does the wall have joists or rafters sitting on it? Is there a strongly oriented 2x8 on top of the wall, where ceiling and roof members tie into that instead of sitting directly on top of the wall?
    – popham
    Commented Nov 6, 2023 at 2:02
  • Yes, please take the tour. All information should be in your post, not down here.
    – isherwood
    Commented Nov 6, 2023 at 17:43

2 Answers 2

1

The fact that there's a 2x8 rim joist running over the window makes it all moot. That acts as a proper header. Carry on.

0

For the 24" window, see Table R602.3(5) from the IRC. Assuming that you have one floor and a non-habitable attic, then the stud spacing requirement is 24". A normal inspector in my area would let it go, but technically you're too wide by 1-1/2" plus your rough opening gaps along the window sides.

For the 28" window, the bending strength of a correctly oriented header is a constant times 1/6(3in)(3.5in)². The bending strength of your header is the same constant times 2/6(3.5in)(1.5in)². Taking the ratio, your header has 43% of the correct header's strength. Guessing at your snow load, building width, and header position within the building, IRC Table R602.7 provides a 3'-1" maximum span length. Assuming that this table value was predicated on a midspan point load instead of a uniformly distributed load, where that's a plausible assumption, length scales linearly with strength and that 43% implies a maximum span length of 0.43(37in) = 15.9in.

Depending on your snow load, etc., your maximum span length could easily be less than that. An inspector should reject it. If it's off-the-books, I would look at the rafter position above the header. All rafters sitting within 5" of the inner jack studs (based on IRC R602.3.3)? I would call that good (probably after implementing the top plate fastener schedule between the "header" and the existing top plate), but otherwise I would rework it.