I'm getting ready to place my materials order and have a few last details/checks I could use help with. This is for installing a subpanel in a detached pump house. I'm putting a 60 amp two-pole breaker in the main panel (rated 225 amps) and a 60 amp main breaker in the subpanel (rated 125 amps). The distance between panels is 265 feet. I’m planning to run 3 wires (2 hots & neutral) of #2 Al XHHW-2 and 1 wire of #4 Al XHHW (grounding wire), all upsized for voltage drop.
Calculations for proportional increase in grounding wire size are right on the cusp of #6 and #4. Depending on whether I use mm2 or Cmils, NEC Table 8-Chapter 9 suggests different sizes. Since 2-2-2-4 MHF is common I thought I would follow that sizing configuration. But each change (wire size, conduit size etc) seems to add $100 which is adding up. :/
I am using EMT inside buildings and schedule 40 pvc conduit buried in a 30" deep trench. The pvc conduit run will have 3-90 degree sweeps. Two 90's are for turns into and out of trench. The third 90 is where the trench makes a turn toward the pump house. The rest of the run is pretty straight. I’ll have someone feeding at the LB that starts the run at the first sweep. My plan was to use 1-1/4" conduit with schedule 80 sweeps coming out of the ground.
Questions
Would #6 grounding wire be sufficient to be code-compliant? (calculations say I need 26248 Cmils and NEC table lists #6 as 26240 Cmils)
Should I upsize my conduit? Should I use plain or 2' radius sweeps? Conduit fill calculations suggest 1-1/4” conduit. Even where I use schedule 80 (just for two sweeps), that comes back as 34.3% fill. But I’ve only done short indoor pulls before and want this to go smoothly.
What size bare, solid copper wire for EGC running to ground rods from sub? I thought I read that this is sized off breaker not feeder conductors. I also read this needs to be equivalently sized as the EGC running back to the main. It’s only running about 12’ out to ground rods.
Color coding just the terminal ends of the grounded conductor with white tape is code compliant as long it is at least 4 AWG, right?