I have a Square D 100 amp main panel with plenty of capacity left and I am wanting to add a 50 amp outdoor sub panel that is 215 feet from the main panel. The sub panel would have only two 120 volt 25 amp breakers. I only plan to run a 1500 watt livestock tank heater, a possible overhead light and have one circuit open for additional small load on a 25 amp breaker. I was going to run three wires of #4 stranded wire in conduit buried in the ground. Using one for hot, one neutral and one ground. I was going to use a single pole 50 amp breaker in my main panel, but I am not finding a single pole 50 amp breaker to purchase from Square D. Can I use a double pole 50 amp breaker and only hook to one side of it or what other options do I have to feed this sub panel out of the main panel? Thanks, Kevin

4
  • Why use 25 amp breakers? What you are planing to power should be quite happy with 20 amp breakers.
    – crip659
    Sep 9 at 15:45
  • 2
    25A 120V breakers are not only unusual, they can't be connected to any normal outlet. So don't do that.
    – Ecnerwal
    Sep 9 at 15:58
  • 1
    This seems expensively uninformed. By running at 120V to "only have 3 wires" the wires need to be much larger and more expensive, so you're not saving money to save a 4th wire.
    – Ecnerwal
    Sep 9 at 16:03
  • You folks are correct, not sure why I typed 25 amp breakers. 20 would be the max I would need. Largest load that I would expect is 1,500 watts on a circuit. Am I better off just running 240 volts from the main to the sub panel? Sep 9 at 16:35

3 Answers 3

2

Given your actual use case: 20A double (240V) GFCI breaker feeding a 4-wire MWBC is by far the most cost effective way to serve the described loads. Given that one of those loads is "future expansion" already, overkill that makes things cost a lot more is a dubious choice unless you really want to burn money. I would say to go ahead and put the lighting on the other side than the heater, though, in case "future expansion" never happens, at least until it does. The load does not need a 25A breaker, and a 25A breaker can't be connected to an outlet, so it's a mostly useless size anyway.

A 25A double (240V) GFCI breaker would give the same capacity (50A at 120V) as your 50A single, but that might as well be 30A (same required wire size) but either of those lose the special exception for a 20A GFCI protected circuit only needing to be buried 12", so you have to go with full depth depending on type of conduit or direct burial cable.

Of course, if you're willing to buy 210 feet of rigid or intermediate metallic conduit (RMC or IMC) you get to have only 3 wires (the metal conduit is ground) and you only need to bury it 6" to top of conduit (unless going under a driveway.) But it will generally cost more than other options with 4 wires.

1
  • Ecnerwal, maybe I should start over on my original question. If I want to add a sub panel with two circuits that would have loads of up to 2,000 watts and my run is 215 feet, what would you recommend using at the main panel for the breaker and the wire size if bury in plastic conduit? Thank you very much and appreciate the help. Sep 9 at 17:00
1

Use #6 aluminum off a 50A breaker, or #2 aluminum off a 60A breaker.

The distance is very punishing to 120V power, requiring several wire size bumps. The only way #6 is going to work is if you run 4 wires (so a proper 120/240V subpanel).

#2 could work as a 120V-only subpanel with 3 wires.

Unfortunately there is no way to downsize the ground wires beyond the sizes found in cable.

0

If you're sure you only want 2 120 V circuits, could use a double pole 30 A breaker and run three wires (2 hots and neutral) plus ground, then put the two 25 A single pole breakers on opposite hot legs.

3
  • Thanks for the reply, I was wondering if I could get by with only running three total wires, hot, neutral and ground. Sep 9 at 15:40
  • 1
    Running a fourth wire later when you decide you want something else will be a royal pain. Just run the four wires now. Aluminum is cheaper than Cu so use it.
    – Jon Custer
    Sep 9 at 15:51
  • Jon Custer, thanks for the reply. What size alum wire would you recommend for this distance? Since alum will be larger diameter, will I have problems connecting to a 30 or 50 amp breaker? Sep 9 at 16:07