I noticed two that two circuits cut off intermittanly but circuit breaker did not trip. I tested voltage with meter when the the problem was happening and found about five volts on both the incoming and outgoing side of every other breaker. I also tested the two wires coming into and out of the main breaker. One of the main wires going to the main breaker also showed about 5 volts when the problem was happening (tested the main wire before the breaker and coming out of the breaker both showed about 5 volts). When the problem is not happening all wires and breakers show about 115 volts. Does the fact the the voltage of one of the two main hot wiress showed 5 volts before it went into the Main breaker mean that the problem is befire my electric box and therefore the responsibility of the electric company?
UPDATE: Power company came out and said there was a bad connector on the roof. I am assuming it was where the wire from the pole connects to the wire coming into the meter and house. Thanks everyone.