I had gone on vacation and left water heater off. After 3 weeks I turned it on and trying to bring it back on. I saw when burner went ON, the water is dripping every second and have a sizzling sound. After 10 seconds I put it back in off. Is this because of condensation? How would I check if water is leaking ?
Also I see the flag light blinking Two times in every 3 seconds when it was ON.
  • How old is the heater?
    Jun 24, 2023 at 16:47
    As for what the light means, you've not bothered to tell us the make and model of your heater, so no bleeping idea what that means. Edit to provide more details...
    Jun 24, 2023 at 16:48
  • It’s probably 9-10!year old . It’s Bradford white brand. Model RG30T6N
    – PowerTech
    Jun 24, 2023 at 17:57
  • You slipped a digit, evidently. RG130T6N exists. And two quick flashes in 3 seconds means the thermostat is calling for heat, while two flashes in 3 seconds means weak pilot light. s3.supplyhouse.com/product_files/…
    Jun 24, 2023 at 18:19
  • So it means it’s operating normally. But as I mentioned below as well why the pilot light goes off automatically
    – PowerTech
    Jun 24, 2023 at 23:12
You ran it for all of 10 seconds?
Yes, it's almost certainly condensation. You have a tank full of cold water and a flame with water as a significant component of the combustion products in the hot gas exhaust.
If water was not dripping before you lit the burner, it's most probably not a leak. Likewise if water is not dripping (or not at the same rate; depending how much flue is dripping back here, it could take a while to dry out) an hour after you shut it off.
  • So how should i processed now after I waited for 8 hours?
    – PowerTech
    Jun 24, 2023 at 17:58
  • Is it still dripping? If not, turn it on and let it burn (and drip, until it doesn't drip) until the water is hot.
    Jun 24, 2023 at 18:14
  • Why pilot light goes out after 10-15 seconds ?
    – PowerTech
    Jun 24, 2023 at 23:11
    Are you following the procedure in the manual for lighting the pilot? You once again are not providing enough detail, and possibly asking a whole new question, (which should not be done as a comment) in a comment that does not make it clear if you are having trouble lighting the pilot, or if the main flame is lighting and the pilot is then going out.
    Jun 25, 2023 at 0:06