I'm planning to rewire my detached garage to replace an old fuse box and add several more sockets. I plan to get an electrician to swap the fuse box for a modern garage consumer unit and test my wiring but I want to do most of the actual installation myself.
The layout of the garage that I'm rewiring and the load I'm expecting (approximately 11-13 sockets; small electronics and a drill press, nothing high power) suits a radial circuit topology using 2.5 mm² cable into a 20 A MCB. However, the garage fuse box that I'm replacing is connected back to a 16 A MCB in the house, which would ultimately limit the current in this circuit to 16 A. Is there any regulation in the UK that prohibits the use of a higher rated MCB in a garage consumer unit than the total rating of the consumer unit itself as governed by its own connection? Would it in any case be a better idea to use a 16 A MCB in the garage consumer unit circuit so that it's obvious to later users what the real limit of the circuit is?
I can in principle replace the cable from my house consumer unit to the garage if needbe, but I'd rather not.
Here in the US, the main circuit breaker (MCB) is used to protect the installed wiring, not a downstream circuit box or devices. Therefore the MCB must be at least matched to the circuit it's connected to or a smaller (lower amp) breaker. Why you'd do that is nonsensical but it's code legal. In other words, you could connect a 10ga cable (ampacity of 30 amps) to a 20 amp breaker to a sub-panel. Maybe you'd want to do that because of a very long run and to minimize voltage drop but I still see no reason not to match the breaker to the wire size.
In your case you'd have to check with local authorities, but I see nothing wrong with feeding a 20 amp circuit with a 16 amp breaker , your mileage may vary! check with your AHJ to be sure.
  • That makes sense. Seeing an MCB on a consumer unit with a lower rating than the attached cable would just create confusion for the next owner! I'll do some more research but I think you're probably right that it'll be allowed.
    – Sean
    May 7 at 18:56