My main panel in on the side of my garage. It currently has 3 breakers:
  1. Main breaker
  2. A/C breaker
  3. Sump pump breaker.
The main panel goes to a subpanel on the back interior wall of the garage which feeds the house. This panel has no breaker spots left.
I am remodeling my garage and adding lights and various outlets. My question is, how best should I handle these circuits?
  1. Can I add a new panel between the existing main and sub panel - i.e. Sending the main power to this panel first and then on to the second existing panel?
  2. Should I try and use an existing circuit -- there is a switch for an outdoor light already in the garage
  3. Update existing panel -- The panel is not in an ideal spot for wiring the garage when it comes to routing the wires. I have shear walls etc and I don't really want the cables to be visible.
I feel like 1 is the best option here.
Main Panel: main panel
Main Panel Inside: enter image description here
A/C & Sump Pump Conduit: enter image description here
Sub-panel: enter image description here
    It would be good to know how you expect to use the new outlets? If just for the odd radio, might just be able to run off the light circuit in the garage, high power shop tools you will need new circuits(second sub panel). Should do a load calculation if adding outlets for shop tools.
    Mar 19 at 19:29
  • Can you post photos of the existing panels please? Mar 19 at 19:38
    No high-powered tools, 120 should be fine. I actually do see 1 empty slot in the sub-panel. But the wire routing won't be easy for this. I'm not sure either about the new sub-panel. The main wires are actually routed through the garage firewall in the roof. I initially confused it with the A/C wires in back of main panel.
    – Rob Fyffe
    Mar 19 at 20:04
  • @ThreePhaseEel pictures added.
    – Rob Fyffe
    Mar 19 at 20:31
  • +1 for all the photos, makes life easier
    – asinine
    Mar 19 at 21:22
Looking at your meter/main panel, it has two huge strikes against it. First, that's a Zinsco combo panel. They are known fire starters. Second, it's a "Rule of Six" panel which has no proper main breaker. The only overload protection is the NEC Article 220 Load Calculation. You can't add loads to that without redoing the Load Calculation to account for the new loads.
Though it's a big job, I cannot do less than recommend replacement with an appropriate and modern meter+main.
If I were you, I would then come off the meter-main to the new subpanel you have planned, and then onward to the original house's panel.
Alternately you could select a "meter + main + some breakers" panel and have it there at the meter. One favorite type is a "Ranch Panel" which has all that and also "thru lugs" allowing full panel power to go onward to a panel.
I would wild-guess that your present service is 125A or 150A - the power company would know, or your service wire size may tell.
-1
I would highly recommend replacing the subpanel with a much larger panel - minimum 30 spaces. You currently have a 12-space/"24 circuit" panel with "20 circuits" in use and all spaces filled. At the same time, you have a small meter-main with only a few spaces (as is normal for that type of box) and I am a little concerned by the Connecticut Electric breaker as to what type of panel it really is. Connecticut Electric is a replacement brand often used in some problematic panels (e.g., Zinsco). So there are really 3 issues here:
  • Make sure the meter-main is safe. If there is any identification - typically a label inside the front cover - that would help. If this is a known-bad panel type then replacement is a priority for safety. If it is an OK panel type but just some questionable breakers then the breakers can be replaced. And it might turn out to be just fine, but it is definitely worth checking. In any case, I would only consider adding more breakers to this panel as a last resort because space is so limited and replacement is not simple because of the meter.
  • Subpanel size (spaces/circuits/breakers). The ideal thing to do is to replace this panel with a larger one. Minimum 30 space - and larger is even better. Assuming your existing breakers are the correct ones for this panel type (I can't tell - more detail, label from front cover, etc. needed) then getting the same brand/line of panel but in a much larger size makes sense as you would then be able to transfer most (possibly all) of the breakers.
  • Subpanel main breaker. Using a main panel as the new subpanel (even though it will still technically be a subpanel) makes a lot of sense. Typical is to get a large panel with a main breaker included - typically 200A. They normally come with a bunch of "free" breakers, plus if you plan it right you can transfer your existing breakers. The only extra you may need is to add a separate ground bar (depending on the panel) as a main panel can have grounds on the neutral bar but a subpanel must have grounds and neutrals separated. This gives you a disconnect here which helps for future work and sets you up for...
  • Heavy up! You have 100A service. As you add more loads, you may need more power! If you have nearly everything (really everything except AC and Sump Pump) in a bigger, 200A rated, main-as-subpanel, then a future upgrade will only require replacing/upgrading the meter-main (which you may have to do anyway, see above...) and running big feeder cable from the meter-main to this main-as-subpanel.
  • Thanks, I am going to get someone out to investigate. One question, the current exposed metal conduit. Are there any concerns about re-routing this through the studs. I'd like to switch it out for PVC conduit and hide it behind the wall. I have been using stud protectors when doing this with regular 12 gauge wire.
    – Rob Fyffe
    Mar 19 at 21:59
  • Yes, you should be able to route this through the studs. But why switch to PVC? Mar 19 at 22:03