I am running power from my main panel in my basement to a sub-panel in my attached garage. At some point I need to transition from the 2-2-2-4 SER aluminum cable being run perpendicular through my unfinished basement ceiling joists into pvc conduit that feeds up into the sub-panel. While my SER cable was still horizontal, I was going to use a sch 40 pvc type c conduit body for the transition. What kind of strain relief fitting should I look for where the SER cable enters the conduit body through the non-threaded port? Or should I use something else at the end of the conduit stub to make the transition instead of the type c conduit body?

2
  • 2
    I take it here that the conduit length is simply being used to shield the cable from mechanical damage? Dec 25, 2022 at 22:18
  • Yes, just from the basement cable run through the wall and up to the bottom of the subpanel.
    – user149104
    Dec 26, 2022 at 5:37

1 Answer 1

1

The correct fitting for this job is a bell end

When using PVC conduit to protect an adequately supported cable from mechanical damage, the fitting you want to use at the end isn't a conduit body, but a bell end fitting of the appropriate size for your conduit. This provides a clean terminus for your conduit that protects the cable from being abraded on its edge.

2
  • So something that clamps around the SER cable as a strain relief where it enters the conduit isn't needed?
    – user149104
    Dec 26, 2022 at 17:54
  • @user149104 -- as far as I can tell, it is not -- do let me know if your local AHJ disagrees, I'd like to know what Code section they're pointing at to require it! Dec 26, 2022 at 20:09