Round 1 (failed attempt)
The current wiring was originally for an electric stove. I now have a gas stove, and would prefer to not run new cable or replace with a new 120v receptacle. My first attempt at this didn't work. Originally, I capped one of the hots at the outlet and grounded the the other side to the bus bar. Swapped out the Circuit for a single pole 15amp, replaced the receptacle with a 15amp GFCI. And it fried the outlet after a few weeks. I shut off the breaker, when I would flip it back on it would spark! (Im thinking because of the gauge of the wire? And a fried outlet?)
Round 2, Here's what we got
Id like to rewire it back to what it was since Im dealing with heavy wires. And try a 240v -> 120 v adapter.
QUESTIONS
  • How would you solve this if you didn't want to run new cable? (I have no problem changing the breaker/receptacle)
  • Considering the 6 guage wire, Can I replace the outlet with a 240v 15amp and then use the 240v --> 120v 15amp adapter?
  • Is that risker since the thicker wire supports higher current?
  • Should I keep the double pole 60amp circut or a lower amp circuit since the adapter supports 120v 15amps to be plugged into it.
  • Should I use 240v 50amp receptacle w/ a 60amp double pole?
    "would prefer to not run new cable or replace with a new 120v receptacle" You've told us what you don't want to do, how about telling us what you DO want to do? Give us a nice "executive summary" level of what you're attempting.
    Oct 20, 2022 at 12:39
ONLY if it is UL-Listed. UL is the safety agency which writes the product safety rules and certifies equipment to be safe. Anything sold over-the-counter in reputable shops will be UL Listed.
Mail order bypasses the consumer safety agencies, and almost everything in the mail-order channels is dangerous cheap junk from you know where.
OK, that should have worked. The issue was clearly workmanship problems in the work that you did. You should labor to improve your work quality until that thing works. We can help.
You absolutely should not be flying off in a totally different direction and trying new things, least of all with transformers, when you have not mastered the basics yet.
So to start, put up photos of the work done so far, relating to the breaker and the receptacle, and we'll try to figure out what went wrong.
Might be a heavy load on the circuit (from a gas range? Unlikely) or it might be a workmanship problem. The photos will tell and then we can guide you.
I would sit at my desk and pigtail black, white, bare wires onto a 120V receptacle. Then I'd crawl down to the socket and use big red or tan wire nuts, and splice those #12 wires to the matching #6 wires coming out of the wall. I would cap off red.
If I did not have a ground wire, well, I'd have to see what you do have. You might have ground after all. If not, it can be retrofitted.
Then down at the breaker panel, I would swap out the 50A breaker for a 20A 2-pole breaker or dual 20A singles. Why? To fill the empty hole. Can't leave a gaping hole in your panel!
Then I would cap off and insulate red in the panel, place black on the breaker, white to neutral bar and bare to ground bar. (which is sometimes the neutral bar, when in Rome do as the last guy did).
No, all that money on receptacle and adapter would be totally wasted. Figure out why the 120V receptacle did not work.
Even more than that, I have a funny feeling you might not have a proper ground wire. That is not the cause of it not working, but it would make it illegal and dangerous to stick the socket you picked, a NEMA 14-50, there. NEMA 14-50 requires a ground. (or a costly 2-pole GFCI breaker and a "No Equipment Ground" label at the socket).
No, that's not a risk. The risk is in the quality of work issues you are running into. We will work on those.
If you insist on fitting a 50A "NEMA 14-50" receptacle, then it is mandatory to use a 40A or 50A breaker with that. NEC 210.21.
I hope I have talked you of dangerous mail-order adapters. If the adapter is stamped "UL Listed" with a file number, then it will have an internal fuse molded into the adapter (not replaceable) and that takes care of safety for the 15A outlet. UL requires that.
You better get your wiring right and sort out any problems with the appliance, because that fuse is NOT replaceable.
  • "when in Rome do as the last guy did" unless the last guy did it wrong... Neutral and ground on the same bus bars is fine in the main panel, but not so much in a sub-panel. We'd need to know that.
    Oct 20, 2022 at 12:44
The breaker for a 14-50 outlet needs to be 50 amp or 40 amp. Either is allowed, since there is no such thing as a 40 amp receptacle. I would put a 40 amp in place, then use the Southwire adapter since it is specifically designed for this task. Assuming the adapter is well designed and you properly wire in the breaker and outlet, there's no other risk that I see to doing this sort of setup.