The light and fan work perfectly, but I was looking to fix a downstream light that has has no power (as I'm a new homeowner) and encountered this strange situation when I started pulling switches out.

Using a non-contact tester (that I verified works with other wires/outlets in the house), I find no hot wires when the light switch is on (and the lights/fan are on) but when I turn the light switch off (and the lights/fan turn off) one of the wires becomes hot. I'm stumped to how such a configuration could even be possible.

The light switch does work with a ceiling fan (where one switch controls on/off and a remote/cord controls the fans speed).

What could be causing this? It doesn't seem to be reversed polarity or any other electrical term I can think of/find on Google. The house was built in the 1920s, so there could definitely be something old/misconfigured.

EDIT: I got a multimeter and measured the voltage. It has 0 voltage when on and 120 voltage when off. Again, I'm not sure how it could have zero voltage when the light is clearly on.

EDIT Again: Along with this posts answer this post, https://community.smartthings.com/t/wiring-question-why-would-a-switch-have-no-power-when-on-and-power-when-off/39897 helped me realize why the multimeter would show voltage when off but not on.

6
  • 1
    Do you have a multimeter, or just the non-contact voltage tester? Sep 4, 2022 at 21:29
  • in that crammed space the non contact tester will give you false reading.
    – asinine
    Sep 4, 2022 at 21:45
  • Thanks for the help! I only have a non-contact tester, but am getting a multimeter tomorrow. Is there a recommended way to test it with that? The non-contact tester is pretty clear on which wire it is though - unless you're saying that it could give a false positive consistently. Sep 4, 2022 at 21:51
  • @OrionTheHunter -- between which terminals did you make your voltage measurements? Sep 5, 2022 at 14:41
  • @ThreePhaseEel between the two terminals on the light switch Sep 5, 2022 at 14:55

3 Answers 3

7

Using a non-contact tester (that I verified works with other wires/outlets in the house), I find no hot wires when the light switch is on (and the lights/fan are on) but when I turn the light switch off (and the lights/fan turn off) one of the wires becomes hot. I'm stumped to how such a configuration could even be possible.

It's a frame/relationship issue. Electricity is relative. There isn't an absolute "this thing has electricity and this thing does not". A bird can land on a wire and be at 12,000 volts compared to the ground, and the bird doesn't care because the bird isn't on the ground.

If the bird had a non-contact tester and put it on the wire it is standing on, then that wire would read cold/0V. However if the bird reached out and measured another phase wire from its vantage on the one wire, the other wires would read as hot, as would the grounded lightning arrestor.

If the bird flew away and landed on the lightning arrestor line, and then measured the phase wires, then they would all read as hot as you expect.

It's all a matter of perspective and position.

So what if you have acquired a frame of reference of 120V from ground, like the bird? Then all your readings are normal for a properly wired switch. This is one frustrating thing about non-contact testers.

However the other possibility is the switch is miswired to switch neutral. Then if your frame of reference were 0V/ground as you expect, then again your readings make sense.

One way to break this impasse is to run a 3-prong extension cord from a known-grounded outlet such as the electrician's outlet next to the panel. Then measure from the obvious ground pin on the cord socket to the switch terminals with either a 2-probe neon tester, or a voltmeter.

4
  • Thanks, appreciate the perspective! I updated my post with my readings from the multimeter and it says 0 volts when on, 12V when off. It also confirms the hot wire is only present when the light/switch is off. This wouldn't be a hot neutral AFAIK, is that right? Sep 5, 2022 at 14:51
  • Sorry 120V when off* Sep 5, 2022 at 15:13
  • @OrionTheHunter Yes, that indicates the switch was miswired to switch neutral. Or the switch was wired correctly, and wherever it gets its power from is miswired to deliver neutral on black. Sep 5, 2022 at 20:53
  • Thanks to your comment and community.smartthings.com/t/… I figured it out. Appreciate the help! Sep 12, 2022 at 17:18
1

For non-contact tester it has to be at least 1 inch away from other wires, to give you the correct reading.

In you case, you have a switch loop. It is when one wire goes up to the ceiling and comes back as another wire to the switch.

When the switch is ON, the power goes to the load (lamp/fan)

When the switch is off the return wire can carry phantom voltage, just enough to trigger the non contact tester.

2
  • Thanks for the comment. I tested with a multimeter and it confirmed that the one wire is hot only when the switch and light is off. Does that mean my switch loop is intertwined with some other circuit? Sep 5, 2022 at 14:55
  • @OrionTheHunter Thank you, we got one out of the way. Question: How many wires are on that switch.
    – asinine
    Sep 5, 2022 at 17:15
0

I am having a little trouble following this, but, if I understand you correctly, you put the leads of the voltmeter across the two contacts of the switch. If this correct, then you should read zero volts (0 V) when the light is on and 120 V when the light is on. Is this what you are getting?

The reason that you read 0 V across the switch when the light is on is that when the light is on, then the switch is closed. That is, the two contact screws are connnected inside the switch. Current is flowing through the closed switch to the light and the light is on. There would be no voltage drop across the switch because a closed switch has zero resistance and V = IR, where R is 0 ohm.

When the switch is off the two contacts are disconnected from each other and no currect is flowing through the switch and through the light which is in series with the switch. The light is off. When you put the volmeter leads across the two contacts you read 120 V because the line hot into the switch is at 120 V relative to neutral and the switched hot (the other contact) is connected to neutral through the light.

EDIT Measuring the voltage across the switch is not really what you want to do. Rather you want to measure the voltage across the light. You would do this by putting one voltmeter lead on the switched hot contact and the other lead on either a neutral or a ground. There should be a ground available in the box. The voltage from the switched hot to the ground (or even better a neutral if there is one available) will be what you expect: 120 V when the light is on and 0 V when the light is off.