Remodeling a 1970’s era condo. The current dryer receptacle has a NEMA 10-30R on a 30 amp breaker. While we are going to be using gas instead of a 240v dryer, I decided to pull the plate and make sure the lugs were snug and tight.

When I pulled the plate, I found the ground and neutral were both under the same lug which I “think” is supposed to only be for the neutral white wire (see photo).

Question:
If I were leaving the 10-30R receptacle, is this proper or should I pull the ground off the lug and just cap it leaving only the white neutral and both hot phases? I understand that ground and neutral are bonded at the main service panel and have learned bonding anywhere else is wrong in residential wiring.

I’m going to replace it with a NEMA 14-30R receptacle for proper grounding in this case, but would like to understand the issues, if any, of this current install.

enter image description here

4
  • Not proper since 10-XX was hot, hot, neutral, no ground. So it is not wired/connected correctly. With all four wires your choice should be a 14-30, but could use a 6-30 if the neutral wire was not used(capped/wire nut). If had to leave the 10-30 then the ground has to come off, to make it legal(it already was there), but still unsafe.
    – crip659
    Commented Aug 18, 2022 at 21:43
  • @crip659 thank you for the comment. Yes, I’m replacing it with a 14-30, but, wanted the knowledge as to best practice if the 10-30 was remaining in place. If so, I appreciate your guidance to remove the ground.
    – Richard
    Commented Aug 18, 2022 at 22:08
  • It is only legal in the sense it was already there(what they call grandfathered in), and wired correctly, that it could be left there. Even then, inspectors/electricians will hym and haw about it being there. If a new circuit or they found out it was added after 1996(could be wrong on the date) then could be trouble.
    – crip659
    Commented Aug 18, 2022 at 22:24
  • 1
    If the 10-30 were staying, the defect of having the ground and neutral tied would have to be corrected. It should not be cut - just capped off. However leaving it is a terrible idea - the next person may get an electric dryer, and the installer will see the 10-30, tear the 14-30 plug off the dryer and fit a 10-30 plug. This is why 10-30 keeps coming back like a bad penny. Commented Aug 19, 2022 at 4:51

1 Answer 1

3

It's a 10-30 - obsolete, hazardous, should be disposed of.

If you actually have a 4 wire feed to the receptacle box, wired correctly, install a NEMA14-30 and send the 10-30 to scrap, where it belongs. Perhaps hit it with a hammer first to make sure it's scrap metal and not improperly re-used.

Leaving (or installing) a 10-30R where it was not a grandfathered install on cable without separate neutral and ground is wrong, period, so hypotheticals about doing that follow "don't do that" and there isn't a "right way to do it wrong."

3
  • "If you actually have a 4 wire feed" the pic seems to very much show a 4-wire cable. ;)
    – FreeMan
    Commented Aug 19, 2022 at 13:48
  • No kidding. Which is why it's just wrong to have a 10-30 there at all. Ever.
    – Ecnerwal
    Commented Aug 19, 2022 at 14:20
  • @FreeMan thank you for the answer. As indicated in my question, I of course am replacing the obsolete receptacle. I was hoping to better understand what to do when you find a ground and neutral bonded together like that outside the scope of the main service panel? Should they always be separated? Is this dangerous under certain fault conditions?
    – Richard
    Commented Aug 19, 2022 at 14:31

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.