My grounding bus in my subpanel, which is secured to the panel frame, reads 122 VAC to hot phase which is great. I also get 122 VAC from hot phase to neutral bus. Shouldn't I also get 122 VAC +/- from hot phase to the cabinet being that it is bonded to the grounding bus? Instead I get a reading of 1 volt.

4
  • 2
    Make sure you're on to metal and not on paint.
    – JACK
    Commented Aug 14, 2022 at 23:49
  • 1
    Panels are usually painted well. Paint is an insulator. Did you touch bare(non-painted) metal of the panel?
    – crip659
    Commented Aug 14, 2022 at 23:49
  • I installed a brand new panel, passed inspection, etc. so no paint, On a lark, ck’d that panel frame was bonded and seems like it’s not.
    – Roger
    Commented Aug 15, 2022 at 0:42
  • Ah! I see what you mean by painted--not a coat over the new metal. Will recheck on the bare metal. Thanks
    – Roger
    Commented Aug 15, 2022 at 16:32

1 Answer 1

1

You're probably trying to read voltages through the paint on the panel. Try taking the reading from a metal connector screwed into a knockout on the panel and to hot. If you don't get a good reading, then your ground bus isn't connected electrically to the panel.