I am living in Ontario Canada so I am dealing with the Ontario electrical code. I am planning on installing a 240V welding receptacle in my garage. The garage subpanel is fed with a 60A 240V breaker from the main panel in our house. Both my welders pull 40A max at 240V, so to size the circuit properly I think I wire a 50A circuit so the maximum amperage is not more than 80% of rated capacity.
My question is, is there any issue with installing a 50A breaker on a circuit only fed with 60A from the main panel? 50A is more than 80% of 60A, but I'm not sure if this is actually an issue or not. I was hunting around in the Code this morning but I couldn't find anything helpful.
My guess is that there is no issue with it, but because I am not an electrician I really want to make sure I'm doing this right. And FYI, I am not likely to be running the welders at their maximum output often, or at all. If I do, I definitely won't be running other power tools at the same time so overloading the circuit shouldn't be an issue.
Either way I am excited to have more than 15A to play with because that is all I have at the moment. Thank you in advance for your help!
Edit thank you for the speedy responses folks. I will post pics of the nameplates tomorrow. Yes, welders are funky. I have a copy of the 2018 code and it only talks about transformer welders, motor-generator welders, and resistance welders.Both of mine are the inverter type. Maybe the 2021 code will mention them?
Also great point about the future owner potentially using it as a car charger, did not think of that. I am pretty sure all new builds in Ontario now need wiring capable of electric car charging, even if the current owners do not need it.
Here are the photos! The ESAB pulls 38A max and the cheap stick welder pulls 41.