For all things electrical I'd been taught that you want to make sure things are tight, and that problems generally come from something be loose - a loose opening into a box, a loose connection to a terminal, insulation being clamped into a connection with a terminal which could cause the connection with the wire to loosen over time.
Now I'm wondering about staples for runs of NM wiring along joists. To keep these from sagging, they were stapled pretty tight and at pretty close spacing, 12 to 18 inches apart depending if there was an obstacle or curve coming up. 1/2" metal staples were used for NM 10/3 and NM 12/2 on separate runs.
Is it a safety issue to have stapled NM wiring firmly against the joists? No doubt the cable was effectively hit with a hammer a few times in a bunch of places, firming down the staples and pinning the cable between the staple and joist. Looking into this it seems that this may have been a mistake.
If this is a problem, can the staples simply be pulled up and re-applied lighter (or using insulated staples instead) as long as the cable insulation looks intact (albeit probably flatter or scuffed in some places)? Given multiple layers of insulation, I'd think the cable does not need to be replaced from having been impacted a bunch of times, or I'd expect if there is a problem it would be a short circuit which the breaker would indicate once the circuit is energized.