You may want to either talk to the manufacturer or go look at an actual unit in Home Depot.
- The specs of 12.5A, 1800/750 + 1200 only make sense if this is a 240V unit. 1800 (largest of burner 1) + 1200 = 3000W, divided by 240V = 12.5A. So that would point to a 15A or 20A 240V circuit.
- The Home Depot page says Please note cooktop is 240-Volt = 240V
- The downloadable specifications document says 120V. It also says 1000W and 1600W elements. A 1600W element could work with a 20A 120V circuit, but not at the same time as a 1000W element, and a larger circuit is almost always 240V.
- The downloadable installation guide includes:
- Page 6: 240V/3000W, 120V/2600W
- Page 7: MSCTE12BG1 (240V), MSCTE12BG2 (120V) - It looks like the Home Depot page is for the BG1 model. (And why they wouldn't make BG1 = 120 and BG2 = 240 is beyond me...)
- Page 9: Use 8 gauge copper wire - That is typical for a 40A circuit.
- Page 10: A 3-wire or 4-wire, single phase, 120/240 volt, 60-Hz., AC only electrical supply is required on a separate,40-amp circuit fused on both sides of the line. That repeats the 40A and seemingly requires 120/240 whether this is a 120V (obviously should only need 120 = 2 wires + ground) or 240V (should only need 240 = 2 wires + ground). My hunch is they boilerplate copied this from all of their larger cooktops/ovens/etc. where 40A 120/240 (120 for lights/clock/timer - none of that here; 240 for heating) is the normal requirement.
- Page 12: 8 gauge copper wire
- Pages 13 and 14: Typical 3/4 wire 120V/240V wiring diagrams
What I suspect is really going on:
- MSCTE12BG2 is 120V, 20A, and if you use both burners at the same time then you will have limited performance. Do not get this one.
- MSCTE12BG1 is 240V, 20A. That is the one Home Depot appears to be selling. Only needs a 2-wire + ground connection, 12 AWG wire or larger, which you have. However, you will need to switch from a single 20A breaker to a proper double-breaker to get 240V. Then mark the ends of the white wire in your cable with black or red tape to indicate it is being used (legitimately) as a second hot wire.
- All the references to 120V/240V, 8 gauge copper wire, 3-wire/4-wire connections are boilerplate copied from other manuals.
The real proof is in the underside picture on Home Depot:

It shows black/red/green coming out of the metal whip, and it says 240V.