Working on a project where I am planning a 3-gang switch box. The box will be a plastic carlton super blue (53 in³). My fill-math works out fine, but I'm wondering about the practical reality of such a crowded box.
Box will contain:
- 14/2 inbound power (4 in³)
- 14/2 outbound switched-power to fixtures (4 in³)
- 14/2 outbound switched-power to fixtures (4 in³)
- 12/3 outbound to another switch box (6.75 in³)
- 12/3 inbound from another switch box (6.75 in³)
- 2 dimmer switches 14AWG (8 in³)
- 1 4 way switch 12AWG (9 in³)
Total: 42.5 in³
If I did the math right - it seems to add up - but that's a lot of stuff - plus it seem odd to me that a dimmer that takes up a lot of volume is the same fill as a basic pole switch.
Am I going to have a hard time getting that all in and should I consider breaking up the switch boxes.
Note - that the 12 AWG is putting a 4 way into an existing branch that was wired with 12 AWG. 14 AWG is on a new circuit.