I have a light that is controlled with 2 switches. I want to control it with a smart switch, so I bought a "3-Way" smart switch, since that's what the online guide said to get.
The switch I received has 5 cables: Neutral, Live, Ground, T1, and T2.
I opened up the socket to replace the old switch, and found that it was only connected to 3 cables: a white, a black, and a red. I'm not sure how they're wired. I foolishly did not record what was connected to where when I took out the switch, but I THINK the white was connected to a slot labeled "common" on the old dumb switch?
I tried connecting black to "Live," white to "Neutral," and red to "T1". When I turned on the breaker, my smart switch powered up! Great. Except when I told the switch to... well, switch - the light stayed off. I tried using the other of the two switches to manually turn on the light, and it instead killed power to my smart switch, and the light remained off.
What should I connect to where? I have pictures of the switch I want to replace and the other of the 2 switches (which I'd prefer to not replace, but can if it's the only option).
First picture: switch I want to replace Second two: switch I would rather not replace but controls the same light. One of the cables on this switch appears to be running into the back of the other switch in the gang box, which controls a separate light (and is the only switch that controls that light).
enter image description here enter image description here enter image description here
    Blind experimenting like this is a bad idea, because there are many combinations that will work, but then kill you. May 17, 2022 at 3:28
  • @Harper-ReinstateUkraine Can you expound on that? "Then will kill you" as in - "it's wired wrong and might electrocute you" or "start a fire" or...? I'm trying to figure out how to identify what is what so I can connect it properly.
    – user112697
    May 17, 2022 at 3:45
    Yeah, any of the above. There are lots of ways to connect things that will poach a neutral or bootleg a ground, or energize things that should not be energized, especially if some wiring lacks a ground. May 17, 2022 at 3:48
    Also, just to be sure you realize it, in the 2nd & 3rd pics, you do not have a "white" wire connected to the switch anywhere. Those are simply painted white courtesy of lazy painters who can't be bothered to cover the outlet/receptacle boxes before they start spraying their "builder's white" paint everywhere.
    May 17, 2022 at 12:05
    @manassehkatz-Moving2Codidact It's a meross 3-way switch.
    – user112697
    May 17, 2022 at 16:36
TL;DR Put the smart switch in the other location and things should be easier
A typical 3-way switch setup using cables (as opposed to individual wires in conduit) has:
  • Switch 1 = Hot + Travelers
In the first switch box, you will have hot coming from the panel possibly by way of another device and/or going on to another device into the common connector on the switch. That wire will almost always be black.
The other two wires will be part of a 3-wire cable and go to the two other screws on the switch as travelers. The third wire of that cable will be switched hot. Colors are anyone's guess. Harper's recommendation is that the travelers should be labeled with a common color, typically yellow. (Can't use green or white, black is typically hot, red is typically switched hot, so that leaves yellow or blue in most packs of tape.)
The third wire should be connected to the switched hot wire (black) going to the light fixture, and the white going to the light fixture should be combined with other white neutral wires in the box (provided everything is on one circuit breaker).
At the second switch, you will only see 3 wires in one cable. Since that's what you found, that first location you worked on is really the second switch. It has two travelers (match the colors to the travelers on the first switch - clearly one is red, but it isn't clear whether the other one is black or white) and the third wire goes to the common screw as switched hot.
There are a bunch of different ways that a smart switch can work here. But I am pretty sure they will all in the end require either:
  • Smart switch in place of switch 1
That's because it needs power - hot and neutral. It can get that easily in the switch 1 box but not so easily (not impossible though) in the switch 2 box. Depending on the type of switch, it might be able to use the existing switch 2 or it might need to use a secondary smart switch ("remote") as switch 2.
  • Smart switch in place of switch 2 + "wireless remote"
To use the smart switch in place of switch 2, without running any new cables, you will end up with black = hot, white = neutral, red = switched hot. That doesn't leave anything for travelers. Which means your second switch (in the switch 1 location) will have to work without any dedicated switching wires. Depending on the smart switch system, it might be powered directly and communicate wirelessly, it might be powered by battery and communicate wirelessly, or it might be powered directly and communicate over the power (hot) wire to the main smart switch. But you have to get everything "just right" or it won't work at all.
  • This is a fantastic and in-depth response, thank you for providing it! It sounds like the cable that is connected to switch 1 that seems to also be connected to the other switch in that box is likely "hot" - I assume this is the "live" my switch notation uses. Can you verify my understanding? Look on switch 1 for a neutral wire (possibly white but no guarantee) The remaining 2 cables on switch 1 that aren't ground will be the travelers. Switch 2 (the one I originally worked out) should be configured how it originally was.
    – user112697
    May 17, 2022 at 3:46
  • Yes, hot==live. But you're mixing up "cables" and "wires". A cable is typically 2 (black/white) or 3 (black/white/red) wires plus bare ground (all grounds together, so ignored for this conversation). Switch 1 has a hot (from elsewhere) and 2 out of 3 wires of the /3 cable - the cable that goes to switch 2. Elsewhere in the switch 1 box should be a bundle of neutrals, one coming in from elsewhere, one going to the light, possibly more. You connect neutral of the new switch to that bundle (you may need a new larger wire nut). You will not find neutral on any "dumb" switch because they don't May 17, 2022 at 3:54
  • use neutral! But smart switches do. Yes switch 2, initially at least, should be configured as it originally was. But that will depend on the type of smart switch as to whether it can work with a manual 2nd switch or needs a matching remote. May 17, 2022 at 3:55
    I believe my smart switch can use a matching dumb switch, it advertised "only need to replace one". Fingers crossed, anyway. Thank you for helping me identify everything! I'll give this another shot tomorrow.
    – user112697
    May 17, 2022 at 3:58
    Just following up, I managed to get it working! Now to go on to the next problem: a single pole switch I want to replace that doesn't have a neutral in the box... :/
    – user112697
    May 18, 2022 at 1:06
You have to start with understanding the 3-way circuit you are working with.
Now here is a schematic for a 3-way circuit. All 3-way circuits work like this. However it is only one of at least 5 possible wiring diagrams.
Black=always-hot, red=switched-hot, yellow=travelers
Note how there are 2 travelers, and one is hot and one is not. It's that easy, really.
Unfortunately, 99% of real world installations do not use colors like those - and generally "make do" with the default colors of cables. Cables are made in black-white-red. So you will have to figure out which colors are your travelers. You could mark them with colored tape - in fact you are required to mark white wires when they are used as other than a neutral.
Once you have your 3-way circuit mapped, you can take a careful look at the smart switch and figure out which location (IF ANY) will be possible to install the smart switch. You do not get a choice about where that is. The map of the wiring will dictate to you which location(s) are possible, and you have to live with that.
Many smart switches allow you to stick a "master" in the mandatory location and a "smart remote" in the other location, and the smart remote gets the same full-feature functionality as the master. That is how you solve the "I want the smart controls at my preferred location" problem. (your goal was to have smart controls at location X, not to have a dumb switch at location Y).
    Just following up: I managed to get it all working, thanks for the information - the diagram helped a lot!
    – user112697
    May 18, 2022 at 1:05