I have a very old house that at some point many decades ago had its electrical system partially updated (mixed knob and tube in a 70s 200A panel). Part of this upgrade relocated the panel to an interior wall around 3 feet from the meter. There is currently a 2" conduit connecting the meter to the load center, and the load center is surface mounted.

I would like to re-route the entrance wire so it penetrates into the interior wall, then flush mount the load center. I'm working with very limited space (2x4 walls, not enough room to fir it out to at least 2x6), and don't think it would be a good idea to run a large conduit through the wall cavity.

With that in mind, I'd like to just run a single SEU cable of appropriate size between the meter and load center horizontally in that 2x4 wall, with just nail plates protecting it. Is this allowed per the latest NEC?

1

1 Answer 1

2

The NEC would permit this, but Washington State code doesn't

The Washington State electrical code amends NEC 230.43 to prohibit the use of SE cables for service conductors within buildings. Since you don't have enough space in-wall for a conduit, you'll need to install a meter-main and 4-wire (SER) feeder, converting the existing panel into a subpanel in the process. (You should be able to use any EUSERC 200A meter-main for this, as Port Angeles does not appear to be picky about meter sockets.)

2
  • If in conduit it was allowed last time I checked the wac or state exceptions, Oregon has some similar rules, table 1E , stuff
    – Ed Beal
    May 14 at 0:50
  • @EdBeal -- yeah, that doesn't help the OP since they don't have enough room in their wall for a conduit (2x4 at 60% doesn't quite make enough room for a bore sufficient for 2" conduit) May 14 at 0:51