I checked the main breaker out at the meter it reads 240 coming out of the meter from leg to leg and 120 to neutral to hub on each side.
coming out of the of the disconnect breaker I read 120 on each leg to neutral but nothing leg to leg on the breaker it should read 240 leg to leg
the mystery is in my house it reads 120 to neutral on one side and 0 to neutral on the other with main off
and 120 across both legs together
at the lugs supplying the main
with the main breaker on and all circuts on i get wired voltage all over with the 220 water heater off is when it shows the dead leg and normal readings on the side with power
what my question is what would cause the outside breaker to read ok on each leg separately but not 240 leg to leg
and then read nothing on one leg on my main wires and be fine on the 1other leg
if it were a neutral wire problem wouldn't I have problems on both legs inside if that were the case and if it reads ok on neutral to each leg coming out of the meter and 240 together
and 120 each side to neutral coming out of the main breaker but nothing leg to leg and inside show dead on one leg and 120 Leg to leg what could cause this it was fine before today update with all breakers and main off in house outside disconnect returns to 240 across and.house shows 120 on good and 2 across and 2 on bad side to neutral with main off and ,,120 across with main in house on with ,220 breakers off