This is happening to me in a US residence. I’m replacing two light fixtures and both switches. One light has a 3-way switch, the other just a single-pole switch. See crude wiring diagram.

For the following observations, I’ve disconnected all black, white and red wires in both boxes and removed the lightbulbs from the fixtures. There isn’t anything else on either switch than the one light on each but I even removed the switches for these tests.

I turned the breaker back on to carefully investigate. Using a DMM, if I measure the voltage between the hot (coming from the panel) and any other wire in the double gang box except those to the single pole switch, I get about 105VAC. I can understand how there’d be 105VAC between it and the neutral but how can there 105VAC to the other wires that should be feeding the other three-way switch and ultimately the light? I assume the neutrals to the other 3-way switch and light fixture would be about 0VAC since presumably these neutrals wouldn’t be tied anywhere else.

There’s no voltage between any of the wires in the single gang box. Also, I’ve measured the resistance between all the wires in the single gang box and they’re all infinite ohms. Even the blacks, whites and reds are infinite ohms to the ground on both ends. Since there’s infinite ohms, this suggests there’s no short like a screw through a wire in the wall, right?

Still – how can there be 105VAC between the hot and any other wire going to the other three-way switch?

Wiring Diagram

3
  • 1
    Why are you putting a meter on and measuring voltage? Are you having a problem with lights not lighting up? Are they lighting, but dimly? This sounds very much like an XY Problem.
    – FreeMan
    Mar 25, 2022 at 13:32
  • 2
    Good meters will have a mode for measurements like this that present a much lower impedance and avoid the problems of phantom voltages. You can also use testers like a Wiggy, aka a "solenoid voltmeter" which works in the same way. The only thing to watch out for is that these low impedance measurements can draw enough current to trip a GFI, so testing against neutral is fine, but against ground you can trip the ground fault protection.
    – J...
    Mar 25, 2022 at 18:09
  • @FreeMan I'm replacing some old X-10 switches with some UPB ones. The wiring diagram for the UPB three-way switches didn't seem to map to what I was seeing in the boxes. I thought it would be helpful to diagram the wiring for the three-way switch. I fell into the phantom voltage trap due to thinking it'd be good to make sure only the feed from the panel showed a voltage. Confusion mounted when my DMM indicated voltage where I was certain there shouldn't have been any. Mar 29, 2022 at 2:53

1 Answer 1

9

This is the normal confusing issue of voltages with very high source impedance. Also named phantom voltages, which may be a little bit confusing, since the voltage is completely real, but it can't drive enough current through the circuit.

The wires running parallel to other wires for many meters or next to grounded metal conduit or building material build a capacitor which will transfer a tiny amount of AC current. This is why those confusing voltages are seldom measured in DC- nets like 12V= car systems. There are also many parallel wires in cars, and even the metallic body is always close by, but for DC, the capacitance between wires or wires and ground can not conduct any current.

This explains the infinite Ohm value between the wires, since the multimeter measures resistance with DC voltage, often by a 9V battery. The capacitance will only conduct current if fed by AC.

The measured 105V~ can't drive enough current in order to energize a 3 Watt pocket receiver or phone charger, but it can drive enough current through the very sensitive multimeter, which has a high impedance of 1 or even 10 Mega-Ohm.

This is why the impedance of the multimeter must be reduced in order to have a test which matches the condition (i.e., the impedance) of a real power consuming device. That impedance is far less than 1 Mega-Ohm, e.g. 10 Ohm for a hair dryer.

A hair dryer connected parallel to the 2 wires under test will show if the voltage remains nearly unchanged ( = "real" power with very low source impedance = hair dryer works normally), or if the voltage will be reduced to nearly zero ( = the power is only sufficient to show "misleading" voltage values on the multimeter = hair dryer will not work at all).

Or in other words: a voltage of 105V with high source impedance does not qualify for a usable energy source.

The source impedance in domestic nets should be as small as possible, f.e. that impedance would be in the range of ca. 0.6 Ohm.

Undressing a nylon sweater may produce high voltages in the 5000V - range, but nobody has ever been killed by undressing such a sweater, since the source impedance of this static voltage is very high.

In contrast, touching a hot street car wire which can have also 5000V is nearly always deadly, since its source impedance is much lower than the source impedance of the sweater. The factor may be as high as 100 Millions.

3
  • 2
    "nobody has ever been killed by undressing such a sweater" - tell that to people working in ATEX/explosive environments (eg. Sewerage, sewage treatment, mining?, chemical plants etc.) ;-)
    – Limer
    Mar 25, 2022 at 19:49
  • 1
    @Limer In EX-environment, special EX-rated installation is mandatory. And of course, anti-static clothing. Often high humidity levels are maintained as additional measurement. And before ignition levels will occur in the air, fans are started to dilute the air.
    – xeeka
    Mar 26, 2022 at 12:42
  • Wow – thanks for the response @xeeka! I especially like the bit about the nylon sweater. 😊 Turns out it was exactly what you wrote. I saw somewhere a similar question that had to do with phantom voltages and one of those answers suggested to connect the light fixture across the hot and one of the other wires that appeared to have voltage on it. Although the light lit when connected across line and neutral, it did nothing when connected between line and one of the other wires. Thanks again! Mar 29, 2022 at 3:01