There are other versions of this question, but as each panel is distinct it requires that I ask for this particular panel. The panel is of unknown age and the house is from 1926, with remnants knob and tube wiring that were still energized when I moved in.

It's a Cutler-Hammer CH Loadcenter. I can't find a model number of any sort, like a G3040 that would mean '30 slots with 40 circuits'. There's nothing like that. It has a 200 AMP main breaker (CSR2200) and 32 full size breaker slots in it. My best guess is it's an older version of the CH32B200J Loadcenter.

Based on the lack of labeling it seems to predates the Circuit Total Limitation (CTL) rules and the 2008 NEC that dropped the hard limit on slots. So that puts in squarely into the "42" rule as best I can tell. Based on that, and using the formula that I found:

(AMPs * Number of Poles) / 10 = number of circuits

Mine: (200 * 2) = 400, and 400 / 10 = 40

So, can I have up to 40 (or 42) circuits in my 32 physical slots? Is something like the Eaton CHT2020CS (Type CH 20-Amp 1-Pole Tandem Circuit Breaker) going to just click in here without an issue?

I think that CHT is CH-Tandem, thus because the Branch Breaker CH Type column in the attached image label includes type CHT, that I am allowed to use these tandem breakers. But I don't see the little extra tabs that the CHTs expect to stabilize them (image of the bottom of my panel, red arrow). enter image description here

Tabs like on the bottom of this, random panel with tandem tabs: enter image description here

If I CAN do this, and my panel doesn't have any restrictive design (those little tabs) that constrains the physical slot the tandem breaker goes into, is there a preference for where to place them, like at the bottom of the panel, or does it not matter at all? If they are stabilized against other breakers so they don't 'flop around' without the tab are they okay?

And finally, is this panel so old that I shouldn't stress it out? It seems mechanically okay, doesn't look like it's falling apart. Should I be looking at replacing the panel instead of testing its limits with tandem breakers? This is the start of essentially a complete rewire of the house and adding a sub panel in the garage to power some shop equipment. So I don't want to stress this panel out on step #1 if it's not made for it. I'd like to only wince once, only do this one time.

Thanks in advance! Aaron

Main label on inside of panel door.

Other part of label

2
  • What year was this installed? That will help as I can’t read much on my phone.
    – Ed Beal
    Jan 25, 2022 at 2:10
  • 1
    Your panel is far newer than you think -- it's a 1997 model at the oldest, based on the panel features and the dating info in the Eaton Loadcenter Aftermarket Solutions Catalog Jan 25, 2022 at 2:28

1 Answer 1

5

That formula you found, you didn't find it in any part of NEC that applies to residences. If it existed, it would come up in nearly every subpanel installation.

The CTL (Circuit Total Limitation limiting to 42 circuits/panel) rules have been abolished.

The panel interior that you pictured has CTL notches on every bus stab, so it can use CTL tandems (Eaton calls them "twins", I call them double-stuff) in every location. Your panel may vary. But that only affects CTL breakers.

The notches do nothing to stabilize the breaker. Twins click in normally. The notch's only job is a reject feature, which matches a bar on a CTL breaker that prevents its insertion where it does not belong. Prior to the CTL rule nothing had notches, so to support those early panels, they never stopped making non-CTL twins which have no bar.

UL approves labeling and instructions as part of Listing the equipment. Many say the restrictions on the labeling still apply. Eaton supposedly says tandems are now allowed in every space in every Eaton panel, and if the CTL permissive notches aren't there, use non-CTL breakers. I presume they got UL to approve this.

It appears Eaton CHT is the only twin breaker they (still) make, and has no reject bar, so it works both CTL and non-CTL panels. That seems to be Eaton's plan: drop all CTL breakers from the line. They're not done with BR yet, and I hear there are shortages due to COVID.



I don't have any problem with older Eaton CH panels that are in good condition. CH is the finest panel you'll ever find in a residence, setting aside Pushmatic, of course.

The main problem your panel has is not enough breaker spaces, clearly. On a heavy remodel you need to come up to current Codes, and that means piles of AFCI and GFCI breakers on 15 and 20A circuits. Eaton twins/tandems are little help since they are only made single-pole and 15-20A, the very circuits which need xFCI!

A subpanel right there is a fine way to solve that problem.

1
  • Thanks. I wish it had a model number/year of production on it prominently. And I apparently got the shape of the tandem tabs wrong from other forums. But as mentioned mentioned, I need to go AFCI and GFCI, so I might need two sub panels. One for the house, and one for the garage. Thanks for getting me off to a good start on this project! Jan 25, 2022 at 18:47