Attempting to replace a bathroom vanity light fixture, removed the previous fixture and found a rough hole in the drywall with metal clad cable containing only 2 wires (yellow and white) - no ground wire observed and no junction box.

I have been trying to look up the proper way to install the new fixture safely, and am currently under the impression I should install a metal (old work) junction box (as the cable is metal clad) using a connector along with an anti-short bushing and then install the new fixture.

Is this a correct plan and what should I do about the lack of a ground wire?

enter image description here

2
  • 4
    Based on (a) colors yellow/white instead of standard black/white and (b) amount of space around the wires, that looks like flexible metal conduit rather than armored cable. Which also means, but I'm not 100% sure so just a comment and not an answer, that the metal is a valid ground within certain constraints. I'd check continuity metal to white neutral - if it shows good (close to 0 ohm) then with a properly attached metal box I think you're all set. Jan 16 at 5:45
  • 1
    This might be helpful: homedepot.com/p/… you screw that into the cable, then the entire metal box becomes the ground. (There are different sizes, I picked a random one.)
    – Ariel
    Jan 16 at 18:30

1 Answer 1

3

Task completed.

  1. Tested flexible Metal Conduit for grounding, and it was grounded. (written method and video tutorial here)
  2. Used a "3/8 in. Flexible Metal Conduit (FMC) Screw-In Connector" to secure conduit to a "RACO 1-Gang Gray Metal New Work/Old Work Standard Octagonal Ceiling/Wall Electrical Box ", then secured box to a stud. Because the connector separates the wires from the edges of the conduit in its basic construction, I did not use a plastic bushing in this case.
  3. Checked the box grounding with multimeter and confirmed.
  4. Finished with typical ground-to-box, white-to-white, and black(yellow)-to-black connections using appropriately sized wire nuts.
1
  • Well done! Note that if you connect "hot-to-hot" and "neutral-to-neutral", you get around the pesky black/yellow problem. When run in conduit, white & grey are neutral, green (if present) is ground, and all other colors are hot.
    – FreeMan
    Jan 20 at 13:54