I have an older GE PowerMark Load Center, circa 1987. It is the same panel being discussed here - this post has good pics of the panel and markings. (GE Powermark Electrical Panel - What Did the Last Guy Do?)
My problem is different than that poster; My neutral bar (all three levels) is full.
My grounds/neutrals are all mixed on the neutral bar. There is no standalone ground bar.
I don't see anything on the panel marking allowing for doubling up equipment ground wires. In the previously mentioned thread, one contributor states that the panel may predate a doubling marking requirement, and suggests doubling up the grounding connectors. If doubling equipment grounds is permissible, I will probably just do some rearranging (making sure no neutrals and grounds are under the same screw) and call it good. Thoughts?
While I could probably install a TGL2 kit (14 space grounding bar approved for the panel per labeling), I don't know if that will solve my problem completely, especially with any future additions. Any thoughts on putting in a larger ground bar e.g., GE TGK42 (42-space grounding bar for PowerMark Gold centers), and moving most of the grounds to that. I'd bond to the panel with 10/32 screws as suggested, and also a #8/#10 wire back to the neutral bar.