I have a pool side GFCI outlet. I am sure that the LOAD from GFCI goes to pool light switch.

I have connected the backyard string light to this outlet. However since connecting string lights, the GFCI keeps tripping as soon as I connect light to this outlet.

I changed the 15A GFCI receptacle but still same issue.

What I saw was that the “hot” wire from LOAD goes to the pool light switch from GFCI receptacle. So, I removed this hot wire from LOAD and now string lights are working and GFCI receptacle is NOT tripping.

What do you think is the problem? Just the hot wire going from LOAD to pool switch or it could be a bad pool light switch?

Is it ok to operate GFCI receptacle for outdoor string light with LOAD wire removed from GFCI to pool light and capped? Will there be any issue with pool electric shock hazard as the pool light is inside pool water and not connected to GFCI receptacle?

4
  • 1
    The hot from the switch must also be accompanied by a neutral. Where does that go? Did the pool lights ever work? Commented Oct 20, 2021 at 22:45
  • 1
    Thanks for the comments. I left the neutral wire as is in LOAD and connected. Just pulled the hot wire out and capped. Pool light is NOT working.
    – calidiy
    Commented Oct 20, 2021 at 23:23
  • @calidiy -- did the pool light work before you plugged the string lights in? Commented Oct 21, 2021 at 0:26
  • Yes. Pool light was working before. Now since I have disconnected hot wire from LOAD in GFCI, pool light is not working. It makes sense as now pool light switch has no power from GFCI to light switch. I did this so I can have backyard string light. But is it safe to do so?
    – calidiy
    Commented Oct 21, 2021 at 2:09

1 Answer 1

1

If there is no hot line going to the pool light, there is no electrocution danger there, however there is no pool light either. (I would disconnect the Neutral too, just in case).

Are the string lights LED by chance? That could explain why adding them made the pool light circuit trip. The pool light circuit had a small amount of leakage to ground, as in under 4mA, so not enough to trip the GFCI by itself. But if the string lights are LED, the "drivers" that make the LEDs work also have a tiny amount of leakage and combined with the tiny amount in the pool light, added up to be over the threshold for the GFCI detection circuit. If you need the pool light to work, you likely need to change the wiring out to that switch, maybe other components as well.

1
  • Thank you. Yes you are correct. String lights are LED lights. I will disconnect neutral white too as you suggested. At this time, due to festival season, I will continue to use string lights at the expense of pool light as long as it’s not dangerous. And based on opinion here, it does not seem to be dangerous in regards to electrocution. Thank you.